Detailing question

Detailing question

Detailing question

(OP)
This is my first wood job. I need some help.

I have a wood beam atop a steel beam w/ a 3X nailer. The beam is 6.75" wide and the nailer is about 8" wide. The total downward gravity load  is abut 15 k.

Am I right in assuming the area to determine the crushing would be 6.75"x8" ?

Would a single Simpson H2.5A and Simpson A35 be sufficient to hold the beam on the nailer since there is no crushing. The beam is about 40' long and has a deflection of 1.25".

 

RE: Detailing question

Which beam is 6.75" wide, wood or steel? Are they at right angles to each other or aligned? What is the width of the other beam?

RE: Detailing question

Are you sure this is all downward load? If this is from a roof, then there is probably uplift.

RE: Detailing question

If i am not mistaken simpson H2.5 A is a hurricane tie for uplift.  Just ask your boss.  I am not sure what you are asking really.  It is all depend on the finish look too.

Never, but never question engineer's judgement

RE: Detailing question

(OP)
The beams are at right angles to each other. The beam on top of the steel beam (W12x50) is a wood beam (floor beam 6-3/4 x 27). There is no uplift on the wood beam.

RE: Detailing question

I am guessing there has to be some kind of horizontal loads - wind or seismic.

Figure those out and you can design a connection.  One thought is to drill thru I-beam and use lag bolts??  Or weld brackets to I-beam and lag those.

RE: Detailing question

Weld a metal plate to the top of the flange of the steel beam at both sides of the steel beam and thru-bolt the wood beam.

Mike McCann
MMC Engineering

RE: Detailing question

newStruc,
You have two things to check on this connection:
1. The bearing stress at the bottom of the GLB and the 3x8 nailer vs Fc perpendicular. The area would be 7.5"x6.75".
2. The load and design of the connection as required in ASCE7-05 Sections 12.1.1, 12.1.2, 12.1.3 & 12.1.4

These Sections in ASCE7 apply to any materials like wood, steel, reinforced concrete, etc. that the structure is framed with.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources