Canadian Electrical Code Question
Canadian Electrical Code Question
(OP)
Did not know where else to post this as there was no CEC in the engineering code section.
My question come with the spacing of equipment (rule 2-308 and 2-310)
The equipment I have (600V MCC) is rated at 1200A, according to 2-310(2) I need two exits or 1.5 meters.
My question comes with where I take this measurement from, I always thought it was from the open door of the equipment but I was told this is not the case, can anyone confirm where the measurement is taken from? I find the code book foggy at best when reading throught these rules.
Thanks
My question come with the spacing of equipment (rule 2-308 and 2-310)
The equipment I have (600V MCC) is rated at 1200A, according to 2-310(2) I need two exits or 1.5 meters.
My question comes with where I take this measurement from, I always thought it was from the open door of the equipment but I was told this is not the case, can anyone confirm where the measurement is taken from? I find the code book foggy at best when reading throught these rules.
Thanks





RE: Canadian Electrical Code Question
RE: Canadian Electrical Code Question
Does this included space required to actually remove the equipment or just to the drawn out posisiton?
RE: Canadian Electrical Code Question
Some equipment will require additional clearances just to be able to remove parts, but I wouldn't think that would be a factor with an MCC.