Robertson Floor Deck
3
RE: Robertson Floor Deck
3
I have some old Robertson catalogues.
I will be out of town tomorrow, but can scan the info and post when I return.
QL-99 is a large section if I remember correctly.  Do you have any further particulars on your situation?
Mike McCann
MMC Engineering
I do have the load tables, Q-Lock Floors Technical Data Book, but it is 29 pagesa including examples.  Mor particular information would help in getting the right table to you.
You might aslso check out these two ICBO Reports:
1.  #2739 from about July 19(80)?, 19 pages, and
2.  #1388 from November of 1980, 28 pages.
Mike McCann
MMC Engineering
Many thanks for the responses.  The deck profiles are QL-99-18 GA and QL-WKX-18/20 GA.
With 3" flutes.
I'll take a look.
Mike McCann
MMC Engineering
That's perfect!  Thanks so much.  Hope to be able to return the favor someday.
Does anyone happen to have the load table for the 2" deck?  What msquared48 posted back in april is exactly what I need but with the 2" flutes and 20 ga.  Thanks.
I have to go to a meeting this AM, but will look it up, scan and post the tables later today.
Mike McCann
MMC Engineering
To msquared48: I am looking for load tables for the Robertson's QL-99-16 deck with 2" flutes. Could you please post this page also?
Thanks for your help with all this information!
OK.  Will be back soon.
Mike McCann
MMC Engineering