KWH Calculation for Pumps
Dear Electrical Guru's
I am a Chemical Engineer . I do technical consulting for Industrial wastewater treatment. We often run into estimating the KWH/day for the pumps in our treatment plants. The procedure we follow to arrive at the KWH/day is as follows
Pump BHP = (Flow*psig)/(1714*Pump.efficiency)
Line Current, I = (BHP*746)/(1.732*P.F*E*MotorEfficiency)
where 'E" is the Line voltage (120,460,2300,4160 etc.. assumed based on the Motor HP)
where"P.F" is the power factor (0.9 for motors > 50 H.P and 0.75 for motors < 50 H.P)
KVA = (1.732*E*I)/1000
K.W = (KVA*PF)
KWH/day = (K.W * No of hours of Operaton per day)
With above procedure, we notice that the effect of power factor is zero . The reason is that we are dividing the Line current by P.F and then multiplying the KVA by P.F. So the net effect is zero , as we multiply and divide with the same factor, which kinda of says that, there is something wrong in the above formula's that i am following.
Can anyone advice on where i am going wrong. I definetely appreciate a response on the same
Thanx
Naggs
K.W = (KVA*PF)
Thanx
Naggs
RE: KWH Calculation for Pumps
No need to go through other steps since you don't care about line voltage,line current or KVA
Lyledunn