Directly Welded Flange moment connection using partial pen welds

Directly Welded Flange moment connection using partial pen welds

Directly Welded Flange moment connection using partial pen welds

(OP)
Has anyone ever used Directly Welded Flange moment connections with partial penetration welds?  Are there any references to this?

The erector want to field weld the connection but the moment required does not require the weld to be full penetration.

The fabricator does not want to provide flange plates.

RE: Directly Welded Flange moment connection using partial pen welds

I believe you need to provide weld/bolt configuration eith matching the strength of the beam (usually full pen without further verification), or 150% of the required moment strength.

RE: Directly Welded Flange moment connection using partial pen welds

Absent of seismic connections requiring a strength greater than the member capacity, I don't know of any reason why the connection would need to be designed for more than the actual design moment.  Not 150% of the moment, just 100% of the moment.  Use your partial penetration weld and be done.

RE: Directly Welded Flange moment connection using partial pen welds

Because the calculated moment only suggests the likelihood of an event under consideration, not necessarily reflect the true peak force, especially in conjunction with other factors, such as construction practices. If the 150% yields requirement higher than the member strength, then use the member strength as the base for connection design, which is the preferred way.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources