Is there any prescription that say from what voltage or current thermographic scan is relevant? If not, from yours experience can you give some values?
Thank you!
Thank you!
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Thermographic scan
While I lean more to using it for current carrying components, it will also provide effective results for early warnings with faulty arresters where moisture ingress leads to thermal runaway. We've also had good results in checking some of the newer solid dielectric potential transformers.
I don't think there is a limited voltage range for IR. We employ it with transmission voltages of 115, 230 and 500 kV and distribution voltages of 4, 12.5, 13.2 and 34.5 kV.
In a three-phase installation, I think using the maximum temperature is not as important as relying on the comparative temperature on like components on adjacent phases.
RE: Thermographic scan
just remember than an IR scan is a snapshot of the conditions at the time and load conditions when the scan is performed.
if you are going to use it as a predictive tool you need baseline scans for low, normal, and high load conditions in order to detect possible deteriorations of components and connections.
again magoo2 hits a homerun with his last statement on comparative readings.
Steven C
Senior Member
ThirdPartyInspections.com