Shored or Unshored Composite Construction?
Do you generally design or specify shored or unshored composite steel construction? Obviously, each has its drawbacks.
Do you always do one opposed to the other? I'm curious what everyone's thoughts are.
RE: Shored or Unshored Composite Construction?
LOL, there was only one shored job in the offices I worked for. Some un-named engineer accidentally turned on the "Shored" option in RamSteel and the entire job got designed as shored, but constructed as unshored. The error got by the designer, his supervisor who stamped it, the detailer, the shop drawing checker, the fabricator, and the erector. Didn't get by gravity, though. Those 34' long W12x14 didn't stand a chance when they dumped the concrete on there! Pretty large building and it was all in teh air before they discovered the error.
I feel pretty sure if there was a cost savings in shored construction, several of our local contractors would not have hesitated to push for it. They are usually not too shy about those type of things.
Dik
Just be sure to specify the design basis (shored or unshored) in your Structural Notes. Having been around long enough to have experienced what happens when you don't shore floors designed as being shored, you really don't want to see what can happen. Also be sure that the beams' compression flanges are adequately laterally braced, particularly if the metal doesn't provide adequate lateral bracing or there is no metal deck.
Designed a suspended shoring system once for a formed concrete slab + composite steel beam floor - EoR declared the beams did not require shoring. First concrete placement proved otherwise.
Ralph
Structures Consulting
I can see the beam would twist somewhat under the unbalance load from concrete pour. Was that the case?
kslee:
That job goes way back. The problem was one of excessive deflection, both vertically and horizontally. The beams were very light sections and the slab was an early version of post-tensioned concrete. We ultimately shored the beams.
Ralph
For those that design as unshored on a regular basis:
Does the construction load case usually end up governing?
Also, how do you handle the issue of wet concrete ponding during the pour? Do you camber the beam to negate the effect or do you design the noncomposite beam with anticipation of extra concrete?
Does the construction case govern? Depends on your approach. It rarely did with mine. Vibrations often set the member sizes. Camber gets rid of construction DL deflection, so that case is not controlling anything. Increasing member sizes is generally the thing that helps with vibe.
I'm sure some offices see this differently, but that worked well for us and we actually got some compliments from contractors on the designs.
Camber in concrete construction is always an interesting challenge, though I'm not sure how it's handled when placing slabs on metal deck. Many contractors simply use a laser to establish top of concrete being placed. Which will not correlate with cambered members or with beams that do not deflect to level when loaded with concrete. Most contractors are reluctant to use screed rails that control concrete thickness (but not elevation).
Ralph
As a serviceability limit state, it is never required by a spec. or code. It is highly advisable to check on a routine basis for steel-framed floors. If you don't, then sooner or later, you're going to have a floor with complaints. Besides, if you use the FloorVibe software (www.floorvibe.com), it takes probably less than a minute to check for a typical bay.
Floors that are very likely to have lively responses are pretty much any with open-web steel joists and regular composite systems with lightweight concrete, 5.25" slab or thinner. When you get into the normal weight 5.5" or more slabs, vibe is seldom an issue.
Any floor subject to rhythmic activity like dancing or aerobics should be checked. Also, any floor supporting sensitive equipment (microscopes, other imaging equipment, electronics manufacturing, etc.) should be checked. These also take almost no time with FloorVibe.
271828: For concrete on steel beams, I believe the results that you found, assuming the support constraints are reliable when you calculate DL deflection.
My experience has been primarily with all-concrete structures - in that arena the situation is much different, and if you can get a contractor to construct the formwork to the desired concrete element's required camber, your create a problem for finishing the top of the floor. Very often we found that the as-constructed camber did not deflect to level.
Ralph
We cambered a few concrete beams, but we did not measure those.
Occasionally the precomposite load case governs. Just depends on the unique circumstances at each beam.
Similiar to 271828, we camber out 75% of the precomposite dead load. Seems to work out well.
We specifiy for the contractor to place a 'level floor' not a 'constant thickness' floor. Therefore, we assume an extra 1/2" of concrete in our load calcs to account for possible ponding of concrete.
I agree with 271828, you need to check composite steel framed floors for vibrations. You'll find yourself in trouble sooner or later if you don't. We also use FloorVibe for this. Very simple to use program, and can check typical bays in just a few minutes. Good protection against a whole lot of trouble.