Paralleling Transformers

Paralleling Transformers

Paralleling Transformers

(OP)
We are adding a 2nd 150/280MVA auto-xfmr to a 230/115kV substation. The xfmrs are to be run in parallel. Each has a delta tertiary. Through fault impedances are nearly identical on a 150MVA base. The intent is for each xfmr to be on taps so that ideal voltage ratios are identical.
 There is one difference: Due to bus arrangement difficulties, there is a difference in which phase is connected to which bushing:
  Auto 1: A to H1/X1, B to H2/X2, C to H3/X3 (1993 vintage)
  Auto 2: C to H1/X1, A to H2/X2, B to H3/X3 (2008 vintage)
The phasing issue has been worked out.
The design has been questioned by some field people: Someone wondered if some unknown problem might arise, such an interplay of the excitation currents between the two xfmrs. My reaction is that I do not think any problems will arise, but maybe I just have insufficient experience. Does anyone have any experience with a problem that might arise?  

RE: Paralleling Transformers

Are you paralleling the tertiarys??  The installations I have seen did not.  Both were taken into the control building and a transfer switch used on to power critical loads.  

RE: Paralleling Transformers

There will be some, but it should be managable. The problem comes in mainly when you have LTC's on the transformers.

If you are concerned about the LTC: I would think problems would happen if you have significent system unbalance. And with modern theory of not needing to transpose lines that is a real possibility.

This mainly applies to the cross connected CT method, and may not apply to the other methods.
 

RE: Paralleling Transformers

I guess since the phase sequence is d same, there should not be any problem once the CT secondary conections are also connected same in the control panel

RE: Paralleling Transformers

PG&E was paralleling a lot of 400 MVA transformers in Substations.  I cant remember how many taps they had but it was like 12 above and 12 below.  They Load taps and were PLC controlled.  The PLc would switch the taps up and down.
They replaced a set up that used a transforme with minimal taps and an in series voltage regulator ( autotransformer).
I don't remeber seeing the tertiarys paralleled.  

RE: Paralleling Transformers

You must check from rating plate that voltage ratio at all taps are same.Check from test report that impedance between H-L at rated and extreme tappings are same or are within 10 %.In case you want parallel operation on tertiary side,then you should check tertiary limb impedance too. Verify OLTC control scheme for their compatability.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources