Trouble with generator RCD
Trouble with generator RCD
(OP)
Brain picking time (with apologies for length).......
We have a big three phase generator (BG) & a little single phase one (LG). During the day BG runs and supplies a three phase load and a critical single phase load. At night LG runs and supplies the single phase load only.
Both gens have a 30mA RCD on the output and are connected to a panel which starts the BG if LG isn't running. Workers stop LG when they arrive (panels starts BG) and start LG when they leave (panel stops BG). If LG stops in the night then panel starts BG.
Panel gets power from both gens and, via contactors, energises a three phase and single phase output if BG is running and single phase only if LG is running. It has two control transformers (240/110), one fed from each gen, with the 0V of the secondaries tied to earth. This is the only connection between the two systems, contactors have timers to give a 20s dwell between the two single phase contactors at changeover time.
Problem we have is that when BG stops its RCD is tripping. It does it maybe 60% of the time and only if LG is running i.e. if we fiddle it so the panel only thinks LG is running then the rcd stays in.
Both gens claim to have star/neutral connected to earth
Any thoughts welcome
We have a big three phase generator (BG) & a little single phase one (LG). During the day BG runs and supplies a three phase load and a critical single phase load. At night LG runs and supplies the single phase load only.
Both gens have a 30mA RCD on the output and are connected to a panel which starts the BG if LG isn't running. Workers stop LG when they arrive (panels starts BG) and start LG when they leave (panel stops BG). If LG stops in the night then panel starts BG.
Panel gets power from both gens and, via contactors, energises a three phase and single phase output if BG is running and single phase only if LG is running. It has two control transformers (240/110), one fed from each gen, with the 0V of the secondaries tied to earth. This is the only connection between the two systems, contactors have timers to give a 20s dwell between the two single phase contactors at changeover time.
Problem we have is that when BG stops its RCD is tripping. It does it maybe 60% of the time and only if LG is running i.e. if we fiddle it so the panel only thinks LG is running then the rcd stays in.
Both gens claim to have star/neutral connected to earth
Any thoughts welcome





RE: Trouble with generator RCD
I'd be tempted to use a larger time-delayed RCD for the generator E/F protection and provide individual RCDs or RCBOs for personnel protection on the circuits requiring it. You can still meet maximum circuit disconnection time requirements using, say, a 300mA / 100ms delayed RCD but that would not be suitable for personnel protection.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Trouble with generator RCD
To clarify, the sequence is....
BG running and supplying both loads
LG is manually started and powers up its control transformer
Timer fed from this drops out both BG contactors
NC contact on BG contactor powers another timer which brings in LG contactor
NC contact on LG contactor opens the run circuit for BG which then stops.
More often than not as BG stops the rcd trips
RE: Trouble with generator RCD
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Trouble with generator RCD
The control transformer link to earth is on the 0V of the secondary side, no load (apart from the transformer) is connected to BG when the trip happens and the trip only happens when BG is stopping and LG is supplying the single phase load.
RE: Trouble with generator RCD
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Trouble with generator RCD
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Trouble with generator RCD
RE: Trouble with generator RCD
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Trouble with generator RCD
There are none, both generator neutrals come direct to the panel, are used for the control transformers (both completely independent apart from the 0V of both secondaries being tied to earth) and then go to their respective contactors where they are switched (only one in at a time and with 20s dwell on changeover) and leave the panel to feed the critical load.
Re your earlier comment about spikes.....I haven't investigated this yet as site is 200 miles away (a long way for us in the UK). I have see spikes before on generators as they "cough" to a halt but don't see how this would bring out the rcd given that the only thing connected to the gen when it happens is the control transformer