When did the expansion loop is required
4
I have seen the design method of expansion loop from the book but the book can't tell me when the expansion loop is required
Last time I think i can find the answer from ASME code B31.3 but I can't find it
If you know the paragraph in ASME B31.3 or You know the answer is in the other standard please tell me
Best regards,.
GOBLINTECHNIC
NEW PIPING ENGINEER
RE: When did the expansion loop is required
GOBLINTECHNIC
Expansion loops are used to manage expansion and to assure that the piping system is flexible enough to accommodate the expansion without pipe stresses exceeding the allowable stress and stress range prescribed by the Code.
Managing the expansion of the piping system addresses such issues as "pushing" the expansion away from strain sensitive equipment (vessels, rotating machinery, etc.) by using restraints (line stops, guides, supports, etc.) to direct the expansion away from the equipment and toward an expansion loop.
Every piping system is different from all others.  The need for expansion loops will depend upon the "natural" flexibility of the piping system geometry (layout).  If analysis shows that the system is not flexible enough (stresses too high, equipment nozzle loads to great) then the expansion loop (or other piping geometries that provide additional "offset") should be added.
The piping designer must look at the overall piping system layout and find a location for the loop where it will not interfere with other piping systems.  The dimensions for the loop will depend upon the size (and schedule) of the pipe, the material (some stainless steels have a 25 percent higher expansion coefficient than carbon steels), the operating temperature of the system, etc.  Remember that the piping expansion loop is one third of expansion management.  Adequate anchors and guides are also required to allow the expansion loop to be effective.
I would strongly suggest that you search this forum to find previous discussions of expansion loops and I would further suggest that you find previous discussion regarding piping design text books.
Regards, John.
B31.3 will not tell you when a loop is required directly, but limits of allwoable stress and such are of course addressed.
Taking one line alone in a rack for instance, loop locations are normally chosen to limit adjacent pipe support displacements referenced back to an 'anchor', commonly allowing 150mm movement although larger figures may be used. Loop size depends on many factors such as pipe stiffness and allowable stress. These are affected by pipe  diameter, wall thickness, material, elbow radius, temperature and other factors.
There is no simple equation to calculate loop size, although there are many spreadsheets around that use the 'Kellogg', 'Tube Turns' or 'Spielvogel' methods for loop sizing. which give good results.
3
Piping Loops (repeat)
The question:
"How do I determine the location for anchors and the size of an expansion loop?"
My answer:
You want to know how to handle layout problems that involve long runs of pipe, thermal expansion, anchors, guides and ways to compensate for expansion.
This is a basic problem for all novice pipers and is one that is not easy to explain.  However let me try. First, I think you need to look at the whole system and come to a solution based on that whole configuration.
There are four basic options to compensate for thermal expansion in a piping system.  These options are as follows:
1.    Do nothing.  Just allow enough room on the pipeway and let the pipe expand and contract as it will.  It will create its own friction anchors and will "snake" around as required to compensate for the expansion.  This is not a highly recommended option.
2.    Normal configuration.  This is where there are natural changes in direction of pipeways or routing that will compensate for the thermal expansion.   Natural configuration is defined as a basic "L" shape or a "Z" shape.  Anchors and guides need to be installed to prevent the thermal growth in one line from interfering with another.  If all the legs are the right length and the anchors and guides are placed correctly then you will not need additional methods to compensate for the expansion.
3.    Expansion loops.  In long straight runs of pipeways pipe expansion loops are added to compensate for the thermal expansion.  Anchors and guides are required to control the pipe and insure that the loop will work as designed.
4.    Expansion joints.  Expansion joints of various types are made and used to compensate for expansion in piping systems where there are space limitations or natural configuration or loops are not an option.  Systems with expansion joints also require pipe anchors and pipe guides to work properly.
You need to ask yourself:
Where do I have natural turns that can be used to compensate for expansion?
Where do I have branches? And do these branches create potential problems?
Where do I need to add loops?
Where can I place anchors and guides?
What is the distance between the potential anchor points?
Now!
What size loop do I need for the places where natural configuration will not work?
Now, the question is not how much pipe should you have between expansion loops but what size an expansion loop should be for a given distance between anchor points of a line.
The answer to this question is really simpler than would first appear.  Let's say you are doing layout for a "Unit" which branches (west) off the main north/south offsite interconnection pipeway.  The line under consideration is a medium pressure steam line with 8" schedule 40 pipes and a temperature of 450 degrees F.  There are battery limits block valves at the interconnecting pipeway end and the line dead-ends at the other end of the unit.
Your pipeway (or sleeper way) has a specific spacing and width.  We will use 10 pipe supports at a spacing of 25 feet each and a width of 25 feet.  Number the supports from right to left as PS #1 through PS # 10.  You know you need one or more loops.  You also know that the loops need to be supported.  You also recognize that you can use option 1 (above) for some of the header.  So, start out by placing your first anchor two pipe supports in from the dead-end of the unit at PS # 8.  You will let the last 55 feet (+/-) of header to "free expand."   Next move to the battery limits end of the pipeway and place an anchor at PS #1 nearest to the battery limits block valve.
Now look at the distance between the two anchors.  Is this distance less than 200 feet?  If it is less then you should need only one loop.  This loop should be as near to the halfway point between the two anchors as practical.   Our distance between PS #1 and PS # 8 is 175 feet.  The halfway point is between PS # 4 and PS # 5.
The line will run in the first pipeway berth at the far south side of the unit pipeway.  The loop will rest on a support beam on the north side of the unit pipeway and cantilever out about 5 to 6 feet.  This makes the loop with dimensions as follows: a vertical rise up 2' – 6", a leg north of 23 feet, a flat turn and a leg west of 20' – 0", then a flat turn south of 23 feet and a vertical drop of 2' – 6" back into the lines assigned berth.
You have already placed an anchor at PS # 1 and at PS # 8 so the next thing is to place guides.  The guides need to be one pipe support away from the loop.  So the guides are placed at PS # 3 and PS # 6.
This is what I mean by being simpler than would first appear.  90% of the time you can use the "natural landscape" to help to do the loop design instead if worrying about a lot of calculations.
Please note:  this being a steam system it will still need to have a proper check and/or analysis by a qualified Pipe Stress Engineer.