Generator AC Hipotential Test

Generator AC Hipotential Test

Generator AC Hipotential Test

(OP)
I am looking for a detailed written procedure on how to perform an AC Hipotential test on a newly rewound medium voltage generator. If anyone has a generic procedure or can point me in the right direction it would be appreciated.

Thank you.

RE: Generator AC Hipotential Test

Hate to say it but if you have to ask you should probally hire a testing company to do it for you. It is very easy to damage equipment with a hipot if you dont know what you are doing. www.netaworld.org to find a certified testing company in your area.  

RE: Generator AC Hipotential Test

I agree with zogzog. This type of potentially destructive testing is not fit for on-job-training.

RE: Generator AC Hipotential Test

(OP)
Zog,

Rest assured we have the tools and the talent to perform these types of tests.  Thank you for your concern.  We are in the process of reviewing and updating many of our written test procedures, I have always found it helpful to gather input from other sources when doing this.

This is a very diverse group of electrical power professionals. If there was a written step by step procedure for performing AC hipotential tests on generators, it would be here and may prove helpful to me.

 

RE: Generator AC Hipotential Test

You are going to have a hard time with power frequesncy AC hipot testing on a large generator, ANSI/IEEE Standard 95 is the procedure for DC hipot testing of Genarators >2300V.  

RE: Generator AC Hipotential Test

(OP)
Zog,

Sorry for the confusion, I must not have been clear enough.

We own (9) Series Resonant tests sets rated from 20kV-50KVA to 250kV-1500KVA.  This equipment is designed specifically for testing large generators and/or power cables rated to 345kV.  We have plenty of equipment and plenty of qualified field engineers.  This is not a problem.  

I was just looking for a little help with updating our test procedures.


 

RE: Generator AC Hipotential Test

See section 59 here:
http://www.usbr.gov/power/data/fist/fist3_1/vol3-1.pdf

Also there is a blurb in IEEE 62.2 - 2004 with some typical precautions for testing.  IEEE 62.2 also refers to IEEE 4 for test techniques, which I am not familiar with.  

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Generator AC Hipotential Test

(OP)
electricpete,

Thanks for the USBR document, I should have known to look there!  I will peruse IEEE 62.2 for further info.

Thanks for the help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources