Etap Modelling and Fault Level Interpretation

Etap Modelling and Fault Level Interpretation

Etap Modelling and Fault Level Interpretation

(OP)
I have recieved a report that models Ip as 29.5kA and I"k as 11.7kA for an 11kV switchboard. Which rating should be used to determine the 1 second fault rating of the switchboard (29.5kA = 562MVA and 11.7kA = 222MVA)

RE: Etap Modelling and Fault Level Interpretation

Rodmcm,

You are in the "IEC World". That means

Initial sym rms sc current = (I"K)= 11.7 kA
Peak sc current            = (Ip) = 29.5 kA

Therefore, you should take 11.7 kA as the 1 or 3 second rating for the switchboard.

Hope this helps.
 

RE: Etap Modelling and Fault Level Interpretation

(OP)
Thanks for that
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources