I am confused that up to what size "motor feeder cable" can be protected by a motor starter. For example, a 75HP 460V motor needs Size 4 starter. This motor has a full load amperes of 96 amperes, which means that the conductor with ampacity of 96*1.25=120A (# 1 AWG) should be used.
I understand that the size 4 starter will protect the # 1 AWG cable. But what if instead of #1AWG, I use a bigger cable (say 2/0.) Will the size 4 starter have the capacity to protect this 2/0 cable?
Your response will be highly appreciated.
I understand that the size 4 starter will protect the # 1 AWG cable. But what if instead of #1AWG, I use a bigger cable (say 2/0.) Will the size 4 starter have the capacity to protect this 2/0 cable?
Your response will be highly appreciated.






RE: Cable and Starter
You changed the cable, but did you change the load?
If the starter trips at 96A, is the 2/0 cable going to have a problem carrying 96A?
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Cable and Starter
------------------------------------------------------------------------
If it is broken, fix it. If it isn't broken, I'll soon fix that.