I am looking for a way to calculate total cfm an OAS louvre will flow.  Should I just need louvre area and total fan cfm?

RE: OAS cfm from louvre

Determine the per cent free area for the actual louvre being specified (and supplied). Generally, most louvres have a maximum of 50 % free area. Be cautious about controlling outdoor air quantity to maintain a CO2 level. It is better to define a specific amount of O.A. as minimum and have the system adjusted to provide the minimum. Always ensure that each and every occupied area will have at least the minimum ASHRAE rates of outdoor air ventilation (e.g. 20 CFM per person) under all operating conditions

RE: OAS cfm from louvre

For an approximate maximum flow, I use 50% of the nominal size to get free area then size the intake at 650 fpm to achieve max. flow. If you need the exact number, you need the manufactures tables based upon the exact louver and size. Free area vs. size, DP and water carrying velocity varies greatly with louver selection.

RE: OAS cfm from louvre

Noise level is another factor.  Longer blade spans might be inclined to buzz at higher velocities; noise would be appreciably higher; pressure drop starting to get to the steep part of the curve; more rain ingress for intakes.

DrRTU clearly indicated 650fpm (3m/s) above as a max, i'd add that i would be more inclined to design at say 500 fpm (2.5m/s) as the limit for airflow.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources