Space for Breaker in MCC

Space for Breaker in MCC

Space for Breaker in MCC

(OP)
Can someone tell me how much space is required for a breaker in the MCC? I know that the size 1 and size 2 starters require 14" X 20", but I need to know how much space would be required for 100A, 150A, and 225A breakers.

RE: Space for Breaker in MCC

That's what manufacturer's literature is for.  There are no generic answers, you have to find the answer for the specific MCC model and breaker type.  Different breaker types with the same amp rating might take different sizes.

RE: Space for Breaker in MCC

Timm1--

And PLEASE think of the poor electricians who will have to deal with trying to form in the cables suitable for those 100, 150 and 225 amp breakers.  I know some manufacturers who will put a breaker into an MCC can and leave no real way to get the cables to the terminals short of rewriting the laws of nature.

If there's a choice, go with the larger, roomier installation.  Your construction and maintenance folks will have kind thoughts toward you for the next forty years.

old field guy

RE: Space for Breaker in MCC

Further to OldFieldGuy's excellent suggestion, if you need to go larger than normal cable sizes due to voltage drop considerations, make sure you consider terminal strips of appropriate size where possible.

I was involved in an installation whereby the MCC was designed without any consideration of the cable sizes required for the runs. Installation of extra terminal strips in the cable ways to allow appropriate termination was not an option that made anyone happy during construction.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources