pressure drops in valves

pressure drops in valves

pressure drops in valves

(OP)
I am currently trying to use Hevacomp for general pipesizing. My client prefers the output. Manually I have a clear approach but tedious.  When using the software it requests for a K value, fairly ok with this, dimensionless and there are lists from manufacturers. It also requires an acceptable static pressure drop? Both are required for the progression of the software. From experience what would be likely figures for fittings?

RE: pressure drops in valves

Well, if you know the K values then the pressure drop for a particular fitting would be
K*Rho*V*V/2g
where
rho= density in lb/Ft^3or Newtons/M^3
V fluid velocity Ft/sec or M/sec
g= gravitational constant 32ft/sec^2 or 9.8M/sec^2
The answer is in lb/ft^2 or Newtons/M^2 which can be converted  to psi or whatever you Brits use.
For example,   
if a globe valve has a K factor of 1.5 , then for a 1 inch pipe size handling  8 gpm of water which corrresponds to 2.5 ft/sec, the
V^2/2g called the velocity head is
.097 feet and at water's density 62.4 and K=1.5 the pressure drop across the valve is
1.5*62.4*.097=9lb/ft^2=.06 psi
I imagine that if you use the mfr K value, they want to make sure that you are accepting  that value translated to psi drop as a check. So enter any reasonable acceptable value, say .1 psi and see what the program asks. It may say there is a discrepancy and tell you why. I just don't know.

  
 

RE: pressure drops in valves

(OP)
Many thanks. I will try this.  But remember the question rom the software is K? and static pressure? before the pipesizing has been achieved.  Once I have pipesized, I will then have to size my control valves for AHUs cooler coils.   

RE: pressure drops in valves

I can only imagine that a static pressure drop across a valve would apply to a non-return valve which required some minimum pressure drop before there is any flow at all. Once that minimum pressure drop has been overcome a normal K-value would model the pressure drop vs flow behavior.  For a normal shut off or regulating valve (eg gate, globe, ball etc) I would enter 0 as the static pressure drop.

Katmar Software
Engineering & Risk Analysis Software
http://katmarsoftware.com

RE: pressure drops in valves

The way it's worded, it sounds like the software is going to check pressure drop and then if it exceeds your specified static drop, it will upsize the line or the valve.  In that case, if you enter zero, it won't work.

RE: pressure drops in valves

(OP)
And if so what value to enter, or where to look for acceptable values rather than judgement

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources