Does anyone know where to find the min required live loads for a mechanical mezzanine? I have searched ASCE 7 and IBC for it. Myself and my boss recall the loading to be 150 psf, but we cant substantiate a resource to check this....

RE: Mechanical Mezzanine Min Live Loads

ASCE 7-05 appendix C, chapter C4, table C4-1 "Minimum Uniformly Distributed Live Loads":
   Air Conditioning (machine space) 200psf see note a
   Boiler room, framed                 300psf "        "
   Compluter equipment                150psf "        "
   Elevator machine room              150psf "        "
   Transformer rooms                  200psf "        "

Note a: Use weight of actual equipment or stored material when greater.

1994 UBC, Table 16-B "Special Loads" (note 1) line 7. Mechanical & electrical  = Total Loads

Note 1: The tabulated values are minimumn loads. Where other vertical loads required by this code or required by the design would cause greater stresses, they shall be used.

I'd try to get the equipment size and weight and do a layout even if its a guess.  What about concentrated loads?  Depending on the equipment size and spans, 150psf may be a little light.

RE: Mechanical Mezzanine Min Live Loads

(OP)
Thanks SMB.  Much appreciated.

RE: Mechanical Mezzanine Min Live Loads

yes, don't forget to check the deck for concentrated loads (posts from an equipment support frame, etc).

RE: Mechanical Mezzanine Min Live Loads

Yes, 150 psf is typical for Mech MEzzanine, however this can be quickly exceeded when you have Chillers, Cooling Towers and Boilers.  Try and find out what is going up there.

RE: Mechanical Mezzanine Min Live Loads

If all you have is air handling equipment the load will likely be significantly less. Many HVAC units end up in the 50 psf range actual total load and it seems to me 150 psf would be overkill.

RE: Mechanical Mezzanine Min Live Loads

I agree with JLNJ.  When dealing with HVAC you typically end up with much less than 150psf.  Although when we don't know the specific equipment we use 150psf and verify it with the final equipment when it's selected.

If we know it is a large piece of equipment (chiller, boiler, etc.), as Den32 stated, we do not estimate a floor load without getting the load information.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources