ASCE 7-05 Open Buildings - Case A & B
|
RE: ASCE 7-05 Open Buildings - Case A & B
LC A - Worst Case Uplift (or downard)
LC B - Worst Case Moment (due to differential pressures)
Bascially, for Cantilevered Canopies, like Gas Station Canopies, only putting large uplift forces on the surface is only half the game. Most canopy failures occur due to the Moment (look at pictures from Andrew, Hugo, etc.) from differential wind pressures.