Seismic Calcs on Pipe Bridge.
Hello;
I am currently working on a pipe bridge that will support a 20" water line. Total weight of combined system is 36kips.
I am working on the seimic part. I would like to know if I can use the ASCE-07 (chapter 15) and consider it as a Nonbuilding Structure.
From Table 15.4-2 Seimic Coefficients for nonbuilding Structures Not Similar to Buildings.
Response Mod. Factor = 1.25
Overstrenght Factor = 2
Deflection Amplification factor = 2.5
Mapped Spectral Response Accelaration: Ss = 2.543 g
S1 = 0.866 g
Spectral Response Coefficient: SDS = 1.695 g
SD1 = 0.866 g
Base Shear : 61 kips ( ASCE-07 12.8-2)
I have attached a preliminary Sketch.
S1 = 0.866 g
SD1 = 0.866 g
RE: Seismic Calcs on Pipe Bridge.