Question on Equipment Specs

Question on Equipment Specs

Question on Equipment Specs

(OP)
I have the spec sheet from a sanyo split cooling system , and am a bit confused as far as the power input specification:

"Cooling Capacity (BTU/h): 17,500(4,000-17,500)
Power Input         (W)  : 1500/1500(250-1500)"

(http://www.sanyohvac.com/products.php?id=18KS72_18KLS72)

I'm assuming the 1500W is for peak @ 17,500BTU/h and the 250W is for the 4000BTU/h operating capacity??

Similarly, on ceiling mounted units,

"Cooling Capacity (BTU/h): 39,000(9,500-39,000)
Power Input         (W)  : 3890/3830"
(http://www.sanyohvac.com/products.php?id=42TW72R)

and my assumption doesn't seem to hold in this case?? or are the two numbers representing inside unit and outside unit (evaporator/condenser unit)
what am I missing here?

TIA,


 

RE: Question on Equipment Specs

Is this part of the specs?  (Sanyo split system ductless AC, 17000 BTUH)

♦ Power Supply Voltage/Phase/Hz: 230/208V / 1PH / 60Hz
♦ Running AMPS (Cooling) : 7/7.7 (1.2⇔7.7) Variable Speed
♦ Fuse or Circuit Breaker Capacity: 20

If so, your max power is approx 4.6 KW assuming 100% power factor.

RE: Question on Equipment Specs

(OP)
how do you come to the 4.6kW max power? why is that number different than the "power input" and what about the ceiling mounted unit which is a 39,000BTUH unit? sorry for all the questions, I'm a bit confused, and thanks for your help

RE: Question on Equipment Specs

Assuming 100% power factor, watts = volts x amps = 230 x 20 = 4600 (Maximum)  Actual running kw is about 230 x 7.7 =1771 watts.

RE: Question on Equipment Specs

Anoying indeed to have a manufacturer publish performance data for the electrician and not for the engineer.
The solution in such cases: Change manufacturer. Try Mitsubishi, they will give you the nice data that you need.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources