horizontal load on handrail

horizontal load on handrail

horizontal load on handrail

(OP)
The IBC states that a 50 plf be applied to the top rail of the guardrail.  In a 3 span condition, I have seen it applied as a uniform load across the entire rail (3 spans) and I have seen it applied for just one span.  Anybody have a comment on this?  I know that a minimum 200 lb concentrated load is applied anywhere along the rail not concurrently with the uniform load.

RE: horizontal load on handrail

Do it for the worst case.

RE: horizontal load on handrail

I can't comment on the amount of load but I would assume it's similar to what we use in the UK. In terms of the design approach, applying the load to a single span will give a more conservative design moment compared to allowing for continiuty over the supports. In the latter case, the mid-span moment reduces and although you'll now get moments at the supports they would never be greater than the moment at the centre of a single span beam (if you have equal loading and equal spans). Also in terms of constrcution it is not always practical to have one single rail and therefore the single span design takes account of this possibility.    

RE: horizontal load on handrail

Your bigger question should be what country is the hand rail going to be used in?  The worst case loading ranges widely in the world, it will also depend on it usage, will it be used as an anchor point or just a handrail.  From what I have read on hand rail Australia has one of the highest standers.

Chris

"In this house, we obey the laws of thermodynamics." Homer Simpson

RE: horizontal load on handrail

I would set up a spreadsheet or simple computer model with all your load cases input (panel load, top handrail load and one large concentrated point load), and make sure all your elements have capacity for these loads. In our office we try to limit our deflections to H/125 which allows us approximatley 10mm deflection and the top of the posts.

We had to retrofit and new handrail to an existing exit platform at a university and had a not-so-great detail where we bolted the handrail posts to the web of a channel section. The client asked us to come and and have a look at it because in there opinion it "flexed" a little. We went out and gave it a shake and I didn't think it was moving to far.

I can't upload the video, the size must be to large. I will just post a photo instead, the job is in Australia.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources