3 phase 220VAC motor not running properly on 208 3 phase

3 phase 220VAC motor not running properly on 208 3 phase

3 phase 220VAC motor not running properly on 208 3 phase

(OP)
I am having problems at my shop with a new to me clicker press (hydraulic press for die cutting).  The seller assures me that the machine worked perfectly at their shop, but it does not seem to work correctly in my shop.  Basically, the motor spins up fine (yes in the correct direction), but when I go to activate the press, it is really weak.  I can barely punch through paper with a small die.  I did keep a meter on the line to see if there is any droop in voltage, but it is rock solid at 208.  

This is the second machine we tried with the same symptoms.  The plate on the motor reads 220VAC 3 phase 60Hz, 1HP.  I thought that there was a magical 10% rule on this type of motor so that they would operate from 200-240VAC?  Any suggestions on options?  The way I see it, I can either call the power company and see what my options are for getting 220 ($$$$ I am sure), or maybe a transformer setup.  I called Grainger about it and they recommended PN 1H271, and two of them.  How would this work?  Wouldn't I need one on each leg?  Thanks for any help!

RE: 3 phase 220VAC motor not running properly on 208 3 phase

You could easily install a buck - boost transformer for less than 150.00 from grainger or a local electrical supply house.

NYBTG

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Before you do anything else, make sure it is not a dual voltage motor, i.e. 220/440V and you have inadvertently connected it in the 440V pattern. If you do that, you will have only about 25% torque, which is going to make it behave exactly the way you are describing. It's a very common mistake.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Very common! I just trouble shot exactly that problem. A hydraulic power unit that could barely get thru its punch routine.  If you didn't modulate the controls just right you could watch the motor come to a complete stop.

They'd run it that way for a year but were anticipating increased thru-put demands.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 3 phase 220VAC motor not running properly on 208 3 phase

(OP)
It is a dual voltage motor I think.  It has only three wires, but there is a diagram on the wiring housing that looks like this (attached photo of my poor drawing).  It is wired with one phase from my power panel to one lead coming from the motor.  Thanks for the help!

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Sounds like the motor has been rewound and is probably single voltage 460 volt now.   

RE: 3 phase 220VAC motor not running properly on 208 3 phase

from the diagram, and the voltage it is possibly a European motor.  That would make it a 50Hz motor. A motor rated at 220V, 50Hz would be happiest with 264V, 60Hz.
Yes you can boost with 2 transformers. The circuit is called an "Open delta autotransformer" boost and it is the most economical circuit that I know.
If it is a 50Hz motor read further.
Voltages:
Try a 240:48 volt transformer.
On 208 volts that will develop 41.6V.
When you add the 41.6V to the 208V you will have 249.6V
That's close to 95% of the 264V that you want.
Should work.
If it is a 50 Hz motor let me know and I can walk you trough the transformer connections.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Use the lower voltage connection (The Delta shown in at the top of your sketch).

RE: 3 phase 220VAC motor not running properly on 208 3 phase

(OP)
The plate on the motor definitely reads 60 Hz (though it looks like it was stamped twice so I am not sure what the original stamp said.  I am also sure that the motor is European in origin, there appears to be a another stamping on the casing that reads 380/550 (not sure the exact numbers but somewhere around there).  

So I guess I will need help with that transformer circuit!

As for my sketch, I don't have any idea how I would wire it in any of those configurations since there are only three wires coming out of the motor.  I guess I should assume that the three wires W2, U2, V2 are tied to U1, V1, W1 respectively, internally (delta config)?

Thanks again for all the help!

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Honestly, I would not bother trying boost transformers or other such things on a motor when I don't know what voltage it's supposed to be operated with. If it's connected for a voltage higher than 240V then it will just be a waste of time and money. A motor shop should be able to crack it open and give you their best guess as to what voltage it's wound for.

The motor is running on 208V. If the motor is supposed to be 240V, 60hz then it's running at 86% voltage and could produce 75% of rated torque. If it's a 240V, 50hz motor then it's running at 80% of rated voltage and could produce 64% of rated torque. From your description, it sounds like it's almost producing no torque which indicates to me the motor is connected for a voltage greate than 240V.

Finally, call the seller again and find out what their voltage is. If you're not sure about their answer, go visit the site and look for the main voltage as well as any possible step-up or boost transformers they may have been using to run it.
 

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Or get it rewound for the right voltage and frequency.

RE: 3 phase 220VAC motor not running properly on 208 3 phase

"I don't have any idea how I would wire it in any of those configurations since there are only three wires coming out of the motor"

It's where those wires come out of the motor. Remove the cover plate.  There will be a terminal block that those three wires connect with. Six screws and metal jumpers just like you pictured.  Jumpers can be removed and rotated 90 degrees.
 

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Actually, that's a six lead motor, one on each screw terminal.  There are three coils with both ends of each available to connect in wye or delta.

Typically, in the 50hz world, that would be a 190/380V label or today it might be 200/400V.

I would think that, in the delta configuration, you would get good performance even on 60hz at 208V.  I suspect you have it connected in wye which would leave the motor starved for voltage and very low in torque.

RE: 3 phase 220VAC motor not running properly on 208 3 phase

(OP)
I did take off what I thought was the cover plate, and the three power leads came in, and were tied (by wire nuts) to three motor leads. From the small amount I could see it looked like they cam right from coils. The problem with this motor (one of) is that it is cast in a big housing attached to a flywheel so I cannot just take out the motor very easily. I will try to get more pics and info.

I did talk to the supplier again, and he said they have 240 and sometimes as hot as 250.

Thanks again, I am sure we will resolve it!

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Dick,

Wouldn't that be a 220/380 or 230/400V motor for delta or wye respectively?
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Any chance this thing is (almost) single phasing?  Have you checked all 3 phases or have a power monitor on it?   

RE: 3 phase 220VAC motor not running properly on 208 3 phase

To be honest, that's a piece of crap you have got yourself.

From where did you get it? US or non-US. The nameplate has been re-stamped, the connections are sub-standard and there is no cable gland.

If it dsoes not work, just go back to the seller with it. Not worth wasting energy or money on.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Yes, Scotty, your numbers are correct.  But the same principle applies.

RE: 3 phase 220VAC motor not running properly on 208 3 phase

skogs,

Harsh but true. That really does look rough.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Ouch Gunnar...

Team08,
I would say that if you paid for it, you probably paid too much and you should try to return it. If it was thrown in for free, it might be salvageable. But from the looks of it, this thing has been to a rewinder and messed with, so the only way to tell for sure what you have is to take it to one again, which is not likely worth the time and money for a 1HP motor. A used one will likely cost you less.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: 3 phase 220VAC motor not running properly on 208 3 phase

And did anyone notice the 318   550   60HZ stamped on the side of the connection box?
team08, if you decide what voltage to try, I can suggest a transformer connection.
A 240:48V transformer will give you about 250V if fed from 208V.
Probably the closest size will be 250VA.
The 48V winding will have to support full motor current.
That gives 48V x 3.8A = 182.4VA
Check the price and availability on two 250VA transformers and let me know if you want to continue.
BTW today I was hooking up a 112KVA open delta, autotransformer buck transformer to power a group of 480V fans on 600V.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Yeah, I noticed the 550V and couldn't make my mind up about the other marking. It would equate to a motor rated at 460V / 50Hz, which is a weird combination: a standard voltage from the 60Hz world, on a 50Hz motor. I can't find anywhere in the 50Hz world where 460V is a standard voltage, certainly not Italy where this motor originated.

Personally I'd buy a replacement motor from a recognised brand off ebay and dump this mutant motor in the skip or weigh it at the scrap yard. In that size range they're common as dirt and almost as cheap.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: 3 phase 220VAC motor not running properly on 208 3 phase

The Grainger transformers will get you up to 229V. I see that the Grainger models are rated "Buck-Boost" which I forgot to mention. Fairly important.
If you are happy with 229V use the Grainger transformers. No guarantee.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 3 phase 220VAC motor not running properly on 208 3 phase

A pair of Grainger 1H272 will give you 236V.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 3 phase 220VAC motor not running properly on 208 3 phase

I would think you could pick up a good used motor of that frame cheaper than new transformers. You don't know what you have and neither does the person who sold it to you.  I've seen motor plates like that even on new equipment.  Reading  motor current with a clamp on meter might give you some idea what voltage the motor is.  I would just switch motors rather than hang a bunch of junk on.

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Based on the nameplate the motor is an IEC frame 80 B5, meaning round body with B5 (similar to Nema D-flange)
If you are in N.A., there are number of companies that offer replacement. IE: Baldor MVM5550D.

The existing motor really need to be check out, you have no idea of its past life. Remove the motor, find a motor shop
and get estimate (overhall or repair) and cost on a replacement.  Then you have a motor that will run for years.
Also use a good cable-conduit connector too.

RE: 3 phase 220VAC motor not running properly on 208 3 phase

(OP)
Unfortunately, I don't think I can just buy a standard motor since it looks like the odd casting is part of the motor.  You can see it better in this picture.  So maybe I just need to buy some transformers and use it as is for now until the motor dies.  The one other thing I am wondering is perhaps the lower voltage affects the control logic?

Waross, can you give me a hand with what I will need for the transformers?  I have 4 wire 208, but I think the neutral/ground wire is only used to ground the frame.  Not sure if this affects the need for 2 or 3 transformers?  Thanks again guys!

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Without even knowing what the motor voltage is, how would you spec the transformers, which incidentally, are additional components to maintain /that fail and come at a cost.

As others have said here, either buy a new motor matching your requirement or rewind this motor for the right voltage, speed and frequency in a good motor repair shop.

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Ty this link. You probably need diagram B1.
The points to bring out are H1, H-X, and X4.
Connect both H1's to "A"phase.
Connect one H-X to "B" phase and the other H-X to "C" phase.
Poweer the motor from "A" phase, one X4 and the other X4.
Or, use diagram G1, boosting.
I'm very tired today, so if someone challenges my information I'll take another look.
To calculate voltages, first add the primary voltage (240V and the secondary voltage (24V, 36V or 48V).
For example, 240V + 36V = 276V, but we will be feeding 208 rather than 240 so use 208V/240V for a developed voltage of 239.2V.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 3 phase 220VAC motor not running properly on 208 3 phase

Is there not a split between the motor and that casting it's attached to? We still can't see from the picture how exactly it's build. According to an earlier poster it is a standard IEC flange motor meaning it should be bolted onto that casting.

It that casting actually is part of the motor (custom cast drive-end endbell?) yet the rest of the motor is a standard frame size then maybe you could just use the stator of a new motor. You could also use the rotor of a standard frame motor if the rotor has the same shaft end. Piece something together to get the right voltage and a motor you know will work.

Read the third response from itsmoked describing the hydraulic press that was run for years at the wrong voltage. Just imagine how annoying that has been for the operators and how much production time has been lost with it that way. All because the people involved just accepted that's how it was instead of looking into it and getting it working correctly.

I wish you luck with the autotransformers because from your description on how weak the motor is I don't think an extra 40V is going to make it work significantly better. The motor should be running at 70% power. If it was just lacking a little power than maybe...
 

RE: 3 phase 220VAC motor not running properly on 208 3 phase

(OP)
I did put on a clamp meter and read ~3.3A on each leg so it seems to be in spec of what the butchered motor plate says. Maybe the logic in the controller is faulty at the lower 208? I wish I could just try a transformer to see if that solves the problem. At this point I am not convinced that a new motor will solve the problem either. I am at a loss, guess it is time to have it out with the seller. I will let you know how it pans out!

RE: 3 phase 220VAC motor not running properly on 208 3 phase

A Clicker Press has hydraulic load and limit adjustments. Have you ruled out all hydraulic problems?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources