Why is IT earthing the chosen method for MV and HV systems?
 

RE: IT earthing on MV and HV systems

No idea, what is "IT earthing"?

RE: IT earthing on MV and HV systems

IT = a supply with the neutral earthed via an impedance at the source, or with the neutral isolated from earth.

The 'T' is from the Latin word 'Terra' meaning 'earth'. 'I' represents either impedance or isolated. I don't like the duality of the term 'IT' but I didn't make the rules. I don't recall seeing it used much in relation to MV and HV systems, and low voltage IT systems are pretty unusual in the UK.


IT systems are used where there are no line-neutral loads because they provide a means of keeping the prospective earth fault level within reasonable bounds in the case of an impedance-earthed source or reducing it to virtually zero in the case of an isolated system, thus limiting the scale of damage in the event of an earth fault. Impedance-earthed systems are common in industrial plants with a lot of rotating plant because a stator earth fault with a solidly grounded system will usually mean a write-off or major rebuild whereas a similar fault with an IT system usually results in a salvageable motor.

I'll let the utility guys talk about ungrounded systems and reasons why they are used or avoided.
 
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: IT earthing on MV and HV systems

All of our HV is solidly grounded, wouldn't dream of anything else.  Except for an extremely limited number of very specialized applications, all of our MV is also solidly grounded.  There is no neutral run with any of the HV.  Neutrals are run with all of the MV and are multi-point grounded.

So, in answer to the original question, generally they aren't used except for industrial MV systems.

RE: IT earthing on MV and HV systems

The only place I've seen impedance grounding used regularly is for generators. It is used occasionally for industrial low-voltage systems.

Alan
----
"It's always fun to do the impossible." - Walt Disney

RE: IT earthing on MV and HV systems

IT Systems are illegal in the UK Electricity Distribution network under the ESQC Regs. With one exception -on power plants, so long as precautions are taken to prevent danger.

The low voltage 415/240V system is solidly earthed. The 11kV system is either solid or low impedance earthed via a resistor,reactor or petersen coil, the 33kV system is low impedance earthed, and the 132kV (and above)system is solidly earthed.

I'm not sure therefore why oconn thinks IT earthing is the chosen method.
Regards
Marmite

RE: IT earthing on MV and HV systems

Resistance earthing of MV systems with motor feeders is recommended by IEEE141.
This is to minimise stator core damage possibility during motor earth faults.

RE: IT earthing on MV and HV systems

Hi.
In additional to all right answers:
I would recommend read a great SEL docoment
http://tesla.selinc.com/techpprs/6123.pdf.

Shrotly: HV, above 110kV is solidly grounded, MV ( according to SEL document), but in industries MV is (99% of cases) low resistance grounding.
term IT, I see first time for the HV, MV application.
As Marmite wrote, 400/230V is usually also solidly grounded , except a (for example) medical application.

BTW, if I remember right, 132kV with low-impedance grounding  (zig-zag trafo) used in Brazil.

Best Regards.
Slava

RE: IT earthing on MV and HV systems

Hi folks,

Just for your information, in our grid (Chesf, Northeast of Brazil), all 500kV, 230kV, 138kV systems are solidly grounded. But our 69kV system is supplyed from a delta winding conneted tranformer and there is a zig-zag reactor in each 69kV busbar for grounding reference.

Remember that the "guard cable" or "earth wire" which is installed at the top of the trasmission line towers for lightning protection, connects the grounding mesh of system substations and seems to work as a (almost) "neutral wire" for HV grounded systems.

Best regards,

Herivelto Bronzeado
  

RE: IT earthing on MV and HV systems

Just for information - in Russia MV networks are 6kV, 10kV and 35kV (50Hz) networks, and almost all of them are isolated from earth.
Networks above 35kV (that is 110kV, 220kV, 330kV etc) are so-called "effectively-grounded" - i.e. they are grounded via small impedance, almost solidly.
Networks below 1kV (that is 690/400V and 400V/230V) are normally solidly grounded.

That's what we have in Russia.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources