Two Flexhead connections off of a cross?
Two Flexhead connections off of a cross?
(OP)
I am doing an add relocate job and was wondering if anyone had any information on running more than one flexhead connection off of a single outlet. I want to attach them to a 1x1/2x1x1 cross with an upright head on the top and a flexhead hose off either outlet. think this bird will fly?





RE: Two Flexhead connections off of a cross?
RE: Two Flexhead connections off of a cross?
Additionally just shifting one of the outlets to a new mechanical tee would take some demand off that junction but just a sliver, try that alteration in your calculation if its close.
RE: Two Flexhead connections off of a cross?
RE: Two Flexhead connections off of a cross?
I would also say to calc it if you were trying to hard pipe 2 sprinklers from a single outlet as well.
Good luck with it.
Travis Mack
MFP Design, LLC
RE: Two Flexhead connections off of a cross?
See sketch http://
The correct terminology for the fitting is 1"x1"x1"x1/2" cross and not 1"x1/2"x1"x1". Not meaning to be picky on the fitting but it through me at first.
RE: Two Flexhead connections off of a cross?
Travis Mack
MFP Design, LLC
RE: Two Flexhead connections off of a cross?
Having to calc it is a foregone conclusion.
RE: Two Flexhead connections off of a cross?
If the question is: Is this arrangement possible? The obvious answer is yes. Will it work hydraulically? That will have to be determined by calculations.
Travis Mack
MFP Design, LLC
RE: Two Flexhead connections off of a cross?
It's nice to see two guys I respect come to the same conclusion I did. It helps me keep my perspective on what's right or wrong. Thank you.