structural steel connection design
I am working in North America. client/upper management hires a korean detailing company for structural steel connection. Their typical shear connection detail is close to shear tab/ beam splice connection. We can use this type of connection as per AISC-ASD manual if we incorporate eccentricity moment in connections(refer.pg3-123- vol.2).
I will explain the detailas follows:
beam stops at the edge of girder flange,shear plate is welded to full depth of girder like a stiffener(it is on both side of web). Two plates similar to splice connection(both side of webs) make a connection between girder and beam using bolts to fulldepth of beam. (this is 100% similar to splice connection).45 mm is distance between beam bolts and face of girder flange.
koreans are using e=45mm eccentricity (for all beams) and Mcon= R*45 KN-mm. My opinion is that eccentricity should be equal to the 1/2 of  flange width of girder (Mconn=.5*gider flange width*R) as beam stops outside of girder flange face.
Now this moment should be resolved into components and victorically added to shear to get max bolt forces.
Please give me your feed back. I would be greatfull to all of you.
RE: structural steel connection design
It appears that the beam bolts are being designed for the 45mm eccentricity.
The eccentricity should be calculated from the girder CG. If you want to be a 100% accurate, then
actual eccentricity = distance of CG of beam bolt group from the girder centroid.
If the 45mm eccentricity is from beam bolt CG to the face of the girder flange, then
eccentricity = ( 45mm + 0.5*girder flange width ) * R
It depends on the the stiffeness of girder and the  connetion plate.
Girder support was torsion resistance. If you consider girder length=0, it's the situation of Korea's calculation.
thanks both of you. 45mm is distance between beam bolts CG and flange face of girder. e= (45+.5*flange width)is it not too conservative.
I am at home and will attach connection detail and some calculations tomorrow to discuss futher.
Girder is modeleld as simple pin connections both sides. Moreover w sections has very little or no torsional resistance. Torsion will act on girder as Mconn (as per AISC) but it would not be resisted by girder instead will be resisted by connection.  once again thanks for your time.
Is there a beam framing into the plate on the other side of the girder web?  If so, the two reactions will tend to remove or at least reduce torsion on the girder.
Best regards,
BA
some time beam is on both side of girder and some time not. It is a typical shear connection configration either beam is there or not.
I can imagine that torsion is there, but it is taken by connection,  not by a girder. My basic worry is this eccetricity moment(how much) and how to resolve it into connection bolts shears.
rfd23,
If the girder cannot take torsion and the beam is connected on one side only the connection must be designed for an eccentric moment of R(b/2 + 45) as noted earlier by both you and slickdeals.
Bolt shears for eccentric loads on bolt groups are readily available.
Best regards,
BA
rfd23,
I do not recognize the beam sizes you are using.  The girder is H390 x 300 with bf = 300.  Does that mean a 390 mm deep member weighing 300 kg per meter with a flange width of 300 mm?  If that is correct, it seems to me that your eccentricity is greater than 150 mm.  There seems to be something wrong with the dimensions shown.
Assuming the distance from the center of the girder to the centerline of the three bolts connecting the beam is 150 mm, then I agree with your calculation, but I suspect it is more.
Best regards,
BA
I agree with the comments above.  The Korean calculation is treating the shear plate like a splice plate, which is incorrect, because it introduces torsion into the supporting girder.  The three bolts at the supported beam should be designed for a much larger eccentricity.
DaveAtkins
I would be calculating the moment that is required to transmit through the splice and resolve the moment into bolt shears. One of the first designs I ever did was a splice very similar to this, I see if I can did it out at work tomorrow.
rfd23,
The bolt spacing is 60 and 70 in your calculation and drawing respectively.  That will help.  Also, the bolts are in double shear which will help a lot.
This detail would not have been my first choice.  I would prefer to extend the beam into the web of the girder, coping the top as necessary, then use an end plate on the beam and bolt through the girder web.  That avoids eccentricity.
Best regards,
BA
I agree with the others that the eccentricity, or lever arm as I would call it, is the distance from the girder web to the bolts in the supported beam.  The connection has to resist the resulting moment and shear.
The only reason for using this detail is to simplify shop fabrication and to reduce slightly the length of rolled steel beams required.  It will be a nightmare to erect, as you have to install all the bolts, including those in the supported beam, while holding the beam in position.  The fabricator is attempting to pass on his costs to the erector.
thanks every body for this usefull discussion. sorry I could not participate earlier.
BA
Beam sizes are as per JIS (Japanese hot rolled section)
beam d=390 bf=300, tf=16, tw=10 mm. weight 107kg/m.
asixth
please check at your work how you did this in past.
hokkie66
it appears to me that this type of connection is normal practice in Korea and Japan. Actually in this particular job fabricator is subcontractor for erector.
I also had a discussion on this in my office and just share with all of you  that this type of connection is also recomended in Japenese code.
Please look at pg3-123 vol.2 ASD manual and discuss. after lot of discussion with you guys and in my office,
I am in favour of taking eccentricity as distance between last bolt line (in this case girder bolts) and weld line (weld to the web of girder). this should be our Mconn as per AISC. e for this particular case would be (15+45)
bolts on both should take this moment and also all plates must be design for this moment.
Please review and discuss.
What is the vertical spacing of bolts...60 mm or 70 mm?  Do you agree that the bolts are in double shear?  What is the distance between the center of girder and the three bolts supporting the beam?  Why am I repeating myself?  Am I having fun?  What other fun stuff could I be doing?
Best regards,
BA
rfd23,
Firstly, for a 300 wide girder, I think the bolt to web distance is greater than that.  It would have to be (150-5-40=105) per your detail.
But that would just give you the moment in the web stiffener, which is OK by inspection, as it is welded to the flanges.  The lever arm for the connection bolts has to be at least the distance between the bolts, which is at least 90 per your detail, but about 200 if you take it to the center of the beam.
If your design is to American standards, you should be dictating the connections, rather than relying on foreign practice.  Where is the actual project located?
hokie66,
The eccentricity has to be approximately (bf/2 + 45) which would be about 195 mm.  The drawing does not reflect this.
I don't believe we are getting very up to date information on this thread.
So how are things in Australia?  Have the fires all died down?  Is anyone waltzing with Matilda?  Have you had any emu stew lately?
Best regards,
BA
BA,
Yes, the fires are gone for now.  Most of those areas have had some rain, so we hopefully won't have any more bad fires until next year.  I see they have reduced the official death toll from over 200 to around 175.  The problem now is flooding in areas on the east coast.  They call it the "Land of fire and water".
Come on down, I'll introduce you to some of the strange local wildlife, the ones we eat and the ones we avoid.
hokie,
Sounds like a plan.  I'd love to come.  We could enjoy some of the local wildlife and maybe a bit of 'bush tucker'.
Best regards,
BA
And we qualified for the world cup
BA
sorry for late response, actually i was in office and did not have internet access to some web sites.
vertical spacing 60mm in calculation is right. detail is for a typical connection (can be differ beam to beam).
Both girder and beam bolts are in double shear. Distance between girder web and beam bolts is 150+5+40.
hookie66
project is in south Africa.
I would take Mconn=R*195
and then resolve this moment by T/C to bolts
T/c=Mcon/lever arm, lever arm is 90 in this case.
I would design all plates to this moment.please advise.
WE are sending our engineer to Korea to resolve these kind of issues.
Thanks everybody for this usefull converstaion.
rfd23,
I agree.  I think we may have misinterpreted your last post.  No matter if the Japanese and Koreans use this detail, I still would not allow it on my projects.  Not compact enough to suit my sense of structural logic.  Good luck with the project.  The joys of worldwide commerce.  Design in North America, project in South Africa, detailing in Korea, fabrication somewhere.  Wow!  You would think whatever savings are achieved would soon be consumed in travel, transport, and miscommunication.
You lost me on the third line.  Where does the lever arm of 90 mm come into play?
Let us say the factored load R is 100 kN.  Then the moment at the three bolt connection to the beam is 19.5 kN-m.  The old fashioned way of doing this would be to say that each bolt takes 100/3 = 33.3 kN vertically.  The top and bottom bolt take an equal and opposite horizontal reaction of 19500/120 = 162.5 kN.  The resultant reaction for each of the top and bottom bolts is 165.9 kN.  One bolt in Double shear is deemed okay.
The modern way of doing it is to consider an instantaneous center.  It is a total pain in the neck to figure out where the I.C. is, so CSA S-16 list a variety of connection configurations along with variable eccentricities and variable pitch.  Unfortunately, the lowest pitch listed is 80 mm so I can't tell you what the shear is with pitch of 60.
For a 3 bolt connection, pitch of 80 and eccentricity of 200, the coefficient C = 0.79 which means that the maximum resultant bolt shear in the group would be R/C = 126.6 kN.  The old fashioned way would yield 129.4 kN, so it appears to be conservative.
Best regards,
BA
BA,
The 90 mm is the horizontal distance between bolts.  His vertical pitch is actually 70, which by the way is what we use in Australia.
hokie,
In his last post, rfd23 confirmed the vertical spacing of the bolts is 60.  I assumed he meant pitch.
If the two lines of bolts are 90 mm apart, then one line is 105 mm from the girder centerline and the other is 195 mm away.  For a reaction of 100 kN, the moments are 10.5 and 19.5 kN-m for each bolt group respectively.  There is no need to check the closer group if it is identical to the more critical one.
The plates connecting the two lines of bolts must be designed for the higher moment, i.e. 19.5 kN-m.
Best regards,
BA
My mistake on the pitch.  I was looking at his original drawing which showed 70.  I agree with your calculation.
BA
I am not sure I am doing it right.
 As per your calculation it appears I am going in wrong direction. I Still want to present it so you can advise me why I am thinking this way.
I would resolve Mcon 19.5 as a couple between two bolt lines(girder and beam)which would be 19.5/90=216KN. 90mm is horizontal distance between girder and beam bolt lines.
This(216) would be my total additional shear on each side of bolts.
for each bolt it would be 216/3+100/3= 72KN<82 KN
82 KN is double shear capacity of single bolt.
As per your calculation (old fashioned way)165KN bolts can not take this (allowable capacity is 82KN-3/4 inch bolt double shear)
please comment on my way of calculation.
Thanks for both of you for your time and usefull thoughts.
I don't think that using eccentricity=45+flang width/2 is a good practice - if the girder is big, let say 3m and the neam is small (W21 or W24).
How to calculation the eccentricity of beam to column connetion?
rfd23,
BA's method is correct.  Think of the top and bottom bolts as the flanges which take the bending.
For the bolt strengths, I think you are talking allowable design, while BA's assumed 100 kN is factored.  Assuming you are using Grade 8.8 bolts (similar to A325), an M20 bolt would take 185 kN in double shear (Australian standard).  Permissible load strength of same bolt was 94 kN.
rfd23,
The shear in the bolts is a matter of statics.  Please look at the attached sketch.
In Case 1, the two members overlap.  The reactions in the two lines of bolts are R(a + b)/b and Ra/b as shown.
In Case 2, the members do not overlap.  Instead, they are connected by a plate which is free to rotate.  The three bolts on the left must carry the moment, R*a and the shear, R.  The three bolts on the right must carry the moment R(a + b) and the shear, R.
The bolt shears in Case 2 are much higher than in Case 1.
Hokie was correct about the factored load.  In Canada, we have been using LSD (Limit States Design) for several years now, so my 100 kN was a factored load.  A 3/4" diameter A325 Bolt has a factored shear resistance of 113 kN if threads are excluded from the shear plane and 79 kN if threads are intercepted.  In double shear, the values are doubled.
I do not like this connection and would try to persuade the steel detailers to use a different connection which does not depend on a group of three bolts carrying the entire moment at that section.  In my opinion, it is not good practice even if it can be made to work.
Best regards,
BA
Add "sum M = 0".
kslee,
He wants to avoid torsion on the girder, so the connection should be designed for the moment based on the distance from the beam bolts to the girder centreline, as advised above several times.  Your method is not appropriate to this connection.  It is a poor connection, none of us like it, but the statics work as BA describes.
Thank you everybody for this usefull inputs.
I myself do not like this connection. I prefered double angle connection direct to girder web as we usued in northamerica. But unfortunately during initial stages of this project, this type of connection was oversees and approved by Leed engineer under pressure(by higher mangement) to meet schedule.
WE can not reject this connection at this stage, however I want to make sure that total number of bolts are enough to take additional moment.
Hokie:
It's not the question of he (rfd) likes it or not, it's his responsibility to accept or reject the connection details. He has some thoughts and doubts on how to look this issue, I was providing my view on how the detail should be analyzed. He needs strong, solid reasons to "REJECT" based on the design code stipulated in the contract document. He has no position to simply say: "I don't like it, do it my way or no way".
Provides rfd is quite prudent, he, as you, did not like it but with doubts in mind. Please help him to clear his mind and this matter in the simplest form you can.
"Clearing his mind" has been done by BA, thank you.  Your supplementary suggestion was unhelpful, as it was incorrect.  In your nomenclature, M= R x(d1 + d2).
You don't have to lecture me on his responsibility.  I know, and he agrees with me and BA that the detail is less than desirable, but it is out of his hands.