what is the longest practical cable length for a 24vdc digital(on/off)siganl ?

I have a Piloteye 2000 flare monitor between 2500ft-3000ft away from control room and need to get digital(on/off) signal to control room. What problems might I encounter ?

RE: 24vdc digital signal cable length limit

The main issue would voltage drop due to current.  If you going to a digital input or small relay, that should not be a problem.  

I'd run shielded twisted pair cable and keep it away from any high current power circuits.   

"The perfect is the enemy of the good." -- Voltaire

RE: 24vdc digital signal cable length limit

I used a successfully used a solid state relay as an interface relay at a distance of nearly a mile from a switched 24V source. It was a solution to someone else's poor design, but worked very well. The key is that the SSR 'coil' - actually an opto-coupler - accepts anything from about 3V DC to about 32V DC as an 'on' state which means volt-drops which would cause problems for an electro-mechanical relay don't bother the SSR. It's worth including a burden resistance of a few hundred ohms or so in parallel with the SRR input to give a definite 'off', especially if you have anything carrying heavy current running along a parallel route.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: 24vdc digital signal cable length limit

I concur with Scotty's OPTO + burden resistor suggestion.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 24vdc digital signal cable length limit

I have gone 1000m (3000 ft) with a standard On/Off signal to a controller.  most controllers take about 45mA to sense a logic (1).  I typically use #14awg for all my digital signals, so that voltage drop issues don't come into play.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources