Magnatizing Current Of Motor

Magnatizing Current Of Motor

Magnatizing Current Of Motor

(OP)
I recently had some experiance with  Eurotherm / Parker 690 VSD drives. To run in Vector control it required a auto tune. But the autotune had to be selected to perform this in stationary mode due to the load. If autotune in stationary mode the drive required the magnatizing current from the manufacturer.
Basically my question, is there a way to calculate this from the name plate if it isn't stamped on the plate?
Manufacturers why do you not put this information on?

RE: Magnatizing Current Of Motor

The no-load current is not stamped in the name-plate (actually it is a good idea and the standards should be revised to include details like no-load current, weight of major components like stator and rotor, bearing details in the nameplate).

All OEM's will have mentioned the no-load current in their test certificates. So, check the TC.

RE: Magnatizing Current Of Motor

I don't know much about the SSD690 but I am surprised it does not have the capability within the drive to measure magnetising current.
I would be cautious about taking the motor manufacturers data in case the motor has been re-wound in its lifetime. This, I would expect, could influence the magnetising current the motor manufacturer may state, if they state at all.

RE: Magnatizing Current Of Motor

(OP)
Thanks for the replies.
Ozmosis i think it does measure the magnetising current, but the drive didn't like autotune in the stationary mode. It wasn't until i put the mag current setpoint in from another drive on an identical motor on the other plant that it would run correctly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources