Reduce design area?
Reduce design area?
I have seen fire sprinkler drawings for a school where the design area was reduced to 900 sq.ft.. Is this permitted by NFPA 13? I could not find it in the 2002 version. Some of the heads were extended coverage, some were standard pendent heads. Coverage density was 0.1 gpm/sq.ft.
Maybe it is a new exception in NFPA 13?
RE: Reduce design area?
Travis Mack
MFP Design, LLC
So, they may still be able to take the QR reduction.
Good luck with the project.
Travis Mack
MFP Design, LLC
So, they may still be able to take the QR reduction."
I'm not sure that I understand this - could the same sprinkler be defined as QR or SR, only depending on the hazard classification?
Normally SR has a 5 mm. bulp and a QR 3 mm. Or am I totally wrong here?
However, based on testing, the EC-11 by Tyco is both SR and QR, depending on spacing and classification. You must read the data sheet very carefully for the criteria.
Good luck!
Travis Mack