(OP)
I have seen fire sprinkler drawings for a school where the design area was reduced to 900 sq.ft..  Is this permitted by NFPA 13?  I could not find it in the 2002 version.  Some of the heads were extended coverage, some were standard pendent heads.  Coverage density was 0.1 gpm/sq.ft.
Maybe it is a new exception in NFPA 13?

RE: Reduce design area?

See Section 11.2.3.2.3 (2002).

RE: Reduce design area?

I believe it has been in since the 99 edition of NFPA 13.  When using QR sprinklers, you can reduce the design area per NFPA 13.

Travis Mack
MFP Design, LLC
 

RE: Reduce design area?

Just make sure they included at least 5 heads in the remote area/calculations.

RE: Reduce design area?

Make sure that the reduced area is also permitted within the local codes because I have run into exceptions that don't allow for certain occupancies to take advantage of this quick response area reduction.

RE: Reduce design area?

(OP)
Quick response, standard coverage heads, K-5.6, are used in some small offices and toilet areas.  The bulk of the open classrooms are TYCO EC-11, extended coverage, NOT QUICK RESPONSE, k=11.2.  I don't think it will fly.

RE: Reduce design area?

Have a good look at the sprinkelr cut sheets. Sometime the EC sprinklers QR vs SR are the same sprinkler (part #, etc). In these cases the only difference is how it is approved to be spaced and calculated in accordance with it's listing.  

RE: Reduce design area?

Tyco EC-11 sprinklers are QR for light hazard applications in spacing of 18'x18'.  They are also QR for light hazard in 20'x20' at certain temps and styles.  The sprinkler is also QR for Ord Haz up to 14'x14' spacing.

So, they may still be able to take the QR reduction.

Good luck with the project.

Travis Mack
MFP Design, LLC
 

RE: Reduce design area?

"Tyco EC-11 sprinklers are QR for light hazard applications in spacing of 18'x18'.  They are also QR for light hazard in 20'x20' at certain temps and styles.  The sprinkler is also QR for Ord Haz up to 14'x14' spacing.

So, they may still be able to take the QR reduction."

I'm not sure that I understand this - could the same sprinkler be defined as QR or SR, only depending on the hazard classification?
Normally SR has a 5 mm. bulp and a QR 3 mm. Or am I totally wrong here?  

RE: Reduce design area?

A sprinkler can be SR with a 3mm bulb.  Fast response and Quick response are different entities.  I believe the 3mm bulb is a fast response (so it can be adjacent to ESFR without draft curtains), but may not be QR.

However, based on testing, the EC-11 by Tyco is both SR and QR, depending on spacing and classification.  You must read the data sheet very carefully for the criteria.

Good luck!

Travis Mack
MFP Design, LLC
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources