Steam loss through failed steam trap calculation
Steam loss through failed steam trap calculation
(OP)
I'm trying to calculate the steam loss (lb/hr) through a failed steam trap. This is for a low pressure steam system operating at 8.5 psig, and the orifice diameter of the steam trap is 5/16". I've come across various examples of calculating the steam loss, with the most common being:
Steam Loss (lb/hr) = 24.24 * Orifice Diameter^2 * PSIA
This is supposedly a variant of the Napier formula. It has been awhile since thermo and fluids class, and I can't recall enough to determine how this formula was derived.
Any tips?
Steam Loss (lb/hr) = 24.24 * Orifice Diameter^2 * PSIA
This is supposedly a variant of the Napier formula. It has been awhile since thermo and fluids class, and I can't recall enough to determine how this formula was derived.
Any tips?





RE: Steam loss through failed steam trap calculation
The industry has used a figure of about 10% of the rated condensate flow as an estimate of steam loss through a failed open steam trap.
RE: Steam loss through failed steam trap calculation
The issue here isn't merely condensate discharging through the orifice. Steam traps don't fail as an open orifice, they also have valve heads and disks that can get in the way periodically. The formula you show is the generally accepted one when the trap is discharging to atmosphere. The losses are typically reduced by an additional 50% when discharging into a closed return. This is a conservative figure used to estimate steam losses in order to evaluate the financial loss and to calculate ROI for projects involving steam trap and steam system repair.
Depending upon how accurate you care to be, you could always put the outlet in a known weight of cooling water, run it for a few minutes with the outlet submerged and weigh the results and temperature rise. Several manufactures have installed ISO test rigs to get even more accurate results, but based upon the accuracy of the measuring instrumentation, you still won't get that last btu.
What I'm saying, run with what you have and it will be fine for 99% of your needs.
RE: Steam loss through failed steam trap calculation
Cheers
RE: Steam loss through failed steam trap calculation
rmw
RE: Steam loss through failed steam trap calculation
Start with the trap vendors
_MJC
RE: Steam loss through failed steam trap calculation
RE: Steam loss through failed steam trap calculation
The purpose of my analysis is not to determine if traps need to be replaced, but to determine the savings that will be seen by replacing failed traps. The projected savings will be used to secure financing.
My original equation and the 10% that steamdog mentioned gives me a result that seems reasonable so I'm just going to go with that.
Thanks guys!
RE: Steam loss through failed steam trap calculation
Get the trap vendor in; He will do all the necessary calculations to justify the new traps and even buy lunch