Lap Splices in Integrity Reinforcement
Is it advisable to allow lap splices in integrity reinforcement in areas other than over a column or its capital?
I would think that any lap splice outside this zone would be ineffective if the slab cracked significantly in the area of the splice. Which one would expect if the slab failed and the integrity reinforcement was engaged.
Please provide links/books with supporting information if possible.
CanadianAce
(P.S. - As the name suggests I am in Canada and am using CSA A23.3-04, but I welcome links to other codes)
RE: Lap Splices in Integrity Reinforcement
I think the ACI and Canadian code probably "sees" a lapped splice (class B splice in ACI) as equivalent to a non-spliced bar.
That said, however, I would tend to see your concern that in a significant failure condition, the lack of direct connection through the splice would be less effective in serving as a suspender for the failed beam.
But I see nothing in the code that states you can't splice them.
I think 318-08 requires Class B splices for all integrity bars and bottom bars spliced at or near support.