Locked Rotor Current Circuit
Is there any method to calculate the locked rotor current of a motor given the T-model circuit parameters?
This is an old motor and the parameters are available, but the performance data is not.  I am simply trying to understand the impact of an across the line start.
RE: Locked Rotor Current Circuit
I assume the T model would be:
==== Z1 ====Z2(s)==
            Zm                   |
Where
Z1 = R1+jX1
Z2(s) = R2/s + jX2
Zm = jXm
If that is a T model, then computing LRC is a very simple  excercize in circuit analysis.
For locked rotor conditions s=1
Ztotal(s=1)= Z1 + (Z2(1)* Zm)/(Z2(1)+Zm)
ILRC = Vterminal/Ztotal(s=1)
If your parameters are on a per-phase basis, then of course the voltage used should be line to neutral voltage.