Gable end wall support
I have been asked by a contractor to engineer a wood garage.  The plan dimensions of the garage are 40'-0" x 60'-0" (clear span) with a required clear height of 16' and a 8:12 roof.  I have already proposed a Metal Building, which doesn't appear to be an option right now.
Before I accept the job, I want to make sure I can get everything to work.  The only problem I can't resolve is how to transfer the loads from the gable ends into the wood roof diaphragms.
I could sheathe the underside of the trusses with plywood (gypsum board is not strong enough) but I don't think the contractor would like that.  I could provide kickers at 2'-0" o.c. but I am not sure if this is the best way to go.
I am just wondering what is the best way to resolve this problem (see attached).
RE: Gable end wall support
I think you've hit on the two most typical options.
1.  diagonal kickers from the top of the lower wall up to the sloping roof diaphragm.
2.  Develop a horizontal truss or diaphragm in the plane of the ceiling line along the bottom of the trusses.  Either the whole ceiling is sheathed and serves OR the first several truss spaces are utilized as a horizontal truss or diaphragm to transfer the lateral force to the side walls.
the kickers are my prefered way of doing it.
JAE is right. you probably wont have to sheath the entire ceiling area, just a few truss spaces in from the gable. design that sheathing like a beam.
I agree with the others here...
2X, 3X or $X Kickers are normally the best option, but use a 4 foot spacing, not 2 feet.  4 to 8 feet is normal, depending on the loads and geometries involved here.  You should be able to develop the connections at the plate and roof levels with no problems with Simpson or similar connectors.
FYI:  Never, but never rely on sheetrock applied to the ceiling structure to resist any horizontal loads.  This is not allowed by code.
Mike McCann
MMC Engineering
Thank you guys.
I have dabbled in wood before but never have gotten a chance to do a full design.  I am figuring this would be an easy structure to start out on.
Msquared48:
I was looking at using a Simpson GBC (Gable Brace Connector) for my end walls.  The information I have states that these are good for 275# - 355# (depending on the angle of the brace).  This is what I was basing my 2'-0" spacing on.  I'm not sure if there is a better connection than a Simpson GBC?
Also, I tend to agree with the note about the Gypsum board, however, if the code gives me allowable diaphragm values then why can't I use those values?  Is this because the code gives values allowable shear in walls and not ceilings?
With regard to your last question, yes.  You will find no horizontal diaphragm values for any sheetrock or gyp sheathing anywhere.
With regard to the GBC, I normally use 1 or 2 A34's, A35's or equivalent that can give me up to 900# per connection.  I have not used the GBC.
Mike McCann
MMC Engineering
Kicker method
He's right, kickers at 24" o.c. is too tight, 48" should work just fine. I've used a variety of Simpson connectors at the intersection of the brace to the wall; doesn't really matter except that it's easy to construct and meets the load requirements. You don't need a connector where the brace meets the roof. Just run some blocking between trusses, and face nail the kicker to the blocking. This gives the framer some leeway.
Bottom chord beam method
If you go this route, don't sheath the underside of the trusses. This might interfere with finishes and it's harder to nail something while holding it in the air.  Provide blocking at 24" o.c. between truss bottom chords and lay the sheathing on top of that. The framer will have to notch around the truss webs, but that's not that bad. Call out a nailing pattern (edge/field) for that decking similar to a diaphragm/shearwall and nail to the blocking AND truss bottom chords.  This method also creates some storage area in the attic.
I hope I understand the question completely.  The way I usually tell them to frame the gable end is using balloon framing.  So I would think if you wood can span to the top of the gable (probably using LVL), then your load will transfer to the sheathing.  Will that solve your problem?
Never, but never question engineer's judgement
ah yes, option 3 that the rest of us forgot to mention.
balloon framing is taking the studs up to the roof (variable height studs). contractors don't like it but engineers do.
I disagree with most of you.  This may be more a geographical thing than technical, but I would never use roof sheathing on such a steep roof as two diaphragms when I can install a flat diaphragm at ceiling level.  The ridge of this thing is 30' high!  Long studs for balloon framing.  If you put the diaphragm where it wants to work, then you only need battens and a metal roof on top.
This will be tricky to erect and maintain stability until the sheathing is in place.  I once saw a similar structure reduced to a big pile of broken lumber when a storm hit at the wrong time.
Done all the time here Hokie, in a moderate wind and high seismic area too.  I've seen some pitches of 14/12 in high snow load areas.  Still standing.
If you want to use plywood on top of the bottom chord of the roof trusses, I have no problem, but the framers will scream.
Mike McCann
MMC Engineering
You wouldn't put it on top of the bottom chord.  How would you fit it in?  As I said, probably a geographical thing.  We don't have snow where I am.  And our building methods are quite different than in the States.
I am really not understanding the building description.  So looking at the gable end description, how high is the apex of the gable end?  I have some ideas how to do this if it is tall.  It is not a typical wood framing but it is all about load path.  If you can proof it, you are good to go.  Explain about the dimension again.
He said it was 16' clear, and 40' wide (I assumed the trusses span 40' rather than 60').  With a slope of 8/12, that gives 13'4" rise in half the width (assuming a central ridge).  Thus my statement above that the ridge is about 30' high.
Hokie66 is correct, as of right now it is approx 30' to the ridge.  I don't believe balloon framing is a possibility with studs that long. They would be too much money and to hard to find.
I'm not sure how much work the contractor has done with engineers in the past.  I would like to have all of my ideas/requirements for building this thing on the table before I start with the final calculations and drawings.  If he doesn't like what I am saying needs to be done then he is free to go somewhere else and I have learned a little about wood framing.
Also, in regards to the roof diaphragm, I know I have to amplify the loads to account for the diaphragm being at an angle (this is in regards to the horizontal wind loads) but do I consider the roof as 2 diaphragms 24'x60' (accounting for the slope) or 1 diaphragm (48'x60')?
You can do something similar to baloon framing.  Is there an openning at the gable end?  If there is, use strong king studs on each side of the opening and some jack studs to take the gravity loading from the header.  Now you need to make the header strong enough to take load from other direction from the wind,  then you put studs above the header that will span to roof diapghram and the header.  If there is no opening, just do a similar framing.  You should be able to cut the stud lenght almost in half.
Now at the top of the 2 king studs you need to be able to transfer it to roof diaphragm.  You can do this by putting some transfer beam at the same 2 locations to connect several trusses until you have enough length to transfer the load with nails.  Since the wind can go both ways, you need to have good simpson connector to connect the king studs to the transfer beams for axial.  I hope I am making any sense.  Like I said, as long as you can justify your load paths then you are good to go.
msquared48:
I was just looking at the simpson A34 and A35 and noticed that they did not give an allowable tension/uplift value for these types of connections.  Since wind loads are produced in both directions how do eliminate the tensile value in the connection of the kickers?
You could use columns at the third points, i.e. 40/3 = 13'4" apart and 16' + 6'-8" = 22'-8" high.  Could probably get by with 6" HSS columns.
Then the top plate (at 16' height)could be beefed up to span horizontally between columns and carry either direct wind or suction pressure.  Bolt top plate to steel gussets projecting from columns.
Best regards,
BA