low power factor

low power factor

(OP)
We have a 1000 kw, 400v, 50 hz generator working for commissioning. Since beginning, we experience low power factor when load is less, typically .45, but when the compressor motor, rated 250 kw, started running, power factor increases to .81. I suggested the cause can be attributed to the temporary feeder cables which at several points where bundled together, instead of usual practice of segregation. Could there be any other reason for this?

RE: low power factor

Power factor is a function of the load, not the feeder cables.

At low load, motors have low power factors.  Power factor goes up as the motor load increases.  

The grouping of the feeder conductor may have a very slight impact on the inductance of the feeder, but tighter bundling would actual lower the inductance.  But these are third or fourth order effects when compared with impact of the load power factor.

"An 'expert' is someone who has made every possible mistake in a very narrow field of study." -- Edward Teller

RE: low power factor

There is nothing wrong with your system.

RE: low power factor

I agree with the above.  As a starting point to understand low generator power factor at low load  you need to consider what is connected to the system at low load and what kind of power is each piece of distribution and utilization equipment consuming.   Transformers at no load draw vars for magnetizing current.   Also... are there real and reactive power interchanged with the grid.  

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: low power factor

Put some duct tape over the power factor meter so no-one can read it and everything will be fine.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: low power factor

(OP)
Thanks for the information, and I believe electricpete had given me an idea since our only load without the compressor motor is the UPS, which is actually seen as a transformer running at very low load at the moment, since only a few circuits had been energized.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources