I'm designing a deck with the following specs:
Height: > 30" above ground
Material: Western Red Cedar (No. 2)
Fb = 575 psi
Fv = 65 psi
Fc (perp) = 350 psi
Fc (parallel) = 825 psi
E = 1.1E6 psi
Joist size: 2x6
I need to come up with a detail for the deck-railing post connection that meets the load requirement in the IRC (R301.5) of 200 lbs.
I have looked at using a Simpson Strong-Tie HD2AHDG deck post connector, however this requires a 2x8 joist size. I also looked at using a DeckLok bracket system. I didn't see anything on their website (www.deck-lok.com) regarding joist size requirement (or type of wood).
Does anyone have any experience with the DeckLok brackets, or do you have any suggestions for a detail I could use for the post connection that will meet the code requirement?
Thanks for your help!
Height: > 30" above ground
Material: Western Red Cedar (No. 2)
Fb = 575 psi
Fv = 65 psi
Fc (perp) = 350 psi
Fc (parallel) = 825 psi
E = 1.1E6 psi
Joist size: 2x6
I need to come up with a detail for the deck-railing post connection that meets the load requirement in the IRC (R301.5) of 200 lbs.
I have looked at using a Simpson Strong-Tie HD2AHDG deck post connector, however this requires a 2x8 joist size. I also looked at using a DeckLok bracket system. I didn't see anything on their website (www.deck-lok.com) regarding joist size requirement (or type of wood).
Does anyone have any experience with the DeckLok brackets, or do you have any suggestions for a detail I could use for the post connection that will meet the code requirement?
Thanks for your help!






RE: Deck-railing post connection
RE: Deck-railing post connection
Keep in mind that you are using a low strength wood. It has low pull-through, pull-out, and flexural strength as compared to others.
RE: Deck-railing post connection
PSlem - the deck is about 4' off the ground. Part of the deck has an overhang (about 2' beyond the beam line), so extending the railing posts to the ground would not be an option on that side of the deck (the railing posts could be right next to the posts supporting the beam, depending on where the rail posts lined up).
Ron - by my calcs a 200 lb load at the top of a 36" railing post will result in a load at the rail attachment to the band joist of approximately 2000 lbs. It's my understanding that carriage bolts are typically used in nonstructural and minor structural applications - I don't think they would be able to handle that high of a load...
RE: Deck-railing post connection
I'd be more concerned about the bending in the wood.
RE: Deck-railing post connection
RE: Deck-railing post connection
I build (as a sideline) the steel posts and wrought iron rails for decks and stairs and interior raling, and anchoring the posts is ALWAYS a struggle. Particularly at stairs where I cannot anchor around a corner as a lateral brace.
For this application, the "standard" OSHA 200 lbf sideways force is actually on the rail as a whole, not on just one post. Your rails (the upper and middle rail) will transmit that 200 lbf load sideways to the post in question and two (at least!) adjacent posts IF the connecting rails are rigid. You should NOT splice your horizontal rails do they DO carry that load, and each rail should be attached "firmly" to each post. (The catalogs you have are great, use them with the screws provided - nails will work loose. Bolts are better. Carriage bolts works OK, but I prefer to use galv oversized washers under the carriage head, rather than let the bolthead sink into the wood. They don't spin if carriage bolt and washer are both galvanized.)
Two 1/2" galvanized bolts in each post are sufficient: this is an outdoors deck and you don't have a finicky homeowner who wants all of her bolts and welds and fasteners to be "invisible" and "never to rust"! (That's "hard" - to say the least.)
Your deck boards extend a good distance away from your beams underneath.
I'd run one 2x6 (or better yet two invisible) beams under the edge fastened to each deck board. Then at each post, use a 3x3x1/4 angle thats cut two boards "long" to clamp the vertical post from underneath to the runner(s) under the deck board. The post load then is supported by several deck boards, and prevented from twisting out by the bolt through the angle iron and the second bolts through the runner beam.
RE: Deck-railing post connection
Further, there is a requirement for 50 lb/lf applied in any direction along the top rail. For post spacings of 48 inches, it is the same as the 200 lb. lateral load. If the spacing exceeds 48 inches, the load on the post goes up.
RE: Deck-railing post connection
RE: Deck-railing post connection
RE: Deck-railing post connection
RE: Deck-railing post connection
RE: Deck-railing post connection
Thanks!
RE: Deck-railing post connection
RE: Deck-railing post connection
http
RE: Deck-railing post connection
My vote is to forget about a force pushing inward as it is not likely to ever occur. And if it does occur from a tree falling, 200# is nowhere near enough anyway.
Best regards,
BA
RE: Deck-railing post connection
The 200 lb requirement is a lateral load requirement. The 50 lb/ft is to be applied in any direction.
RE: Deck-railing post connection
I think the downward push (200#) on rails should also be considered. How often we see people sitting on the rail, and/or standing on the mid-rail to post for photo-op, and to gain better views. This phenomenon is most prevalent in touring areas, parks, schools.... Any thoughts/advise on that?
RE: Deck-railing post connection
RE: Deck-railing post connection
RE: Deck-railing post connection
A 200 lb. concentrated load applied at any point and in any direction, or
A 50 lb/ft distributed load applied in any direction.
They are not to be applied simultaneously, of course.
RE: Deck-railing post connection
Best regards,
BA
RE: Deck-railing post connection
You started well, and concluded well also.
RE: Deck-railing post connection
RE: Deck-railing post connection
I think it is a good design that the post would not fail outward, but inward - a stop sign yells "don't come close !!!".
RE: Deck-railing post connection
RE: Deck-railing post connection
RE: Deck-railing post connection