PLC Relay Outputs Going Bad.
PLC Relay Outputs Going Bad.
(OP)
I have an A-B Micrologix 1000 PLC (1761-L32AWA) with relay outputs which are rated for 2 amps. These outputs control MAC valves. The outputs fail frequently--I'm guessing due to the voltage transients caused by the solenoids, but would they really exceed 2 amps? What kind of surge suppression should I use here? (Manufacturer/cat.# would be very helpful.)
Thanks.
Thanks.





RE: PLC Relay Outputs Going Bad.
But voltage transients do easily exceed hundred of volts. Especially if there are no free-wheeling diodes, snubbers or MOVs.
If your valves are DC, you need a free-wheeling diode or some other device. If they are AC, you need a snubber or varistor, aka MOV.
If you cannot tolerate the dela caused by diodes, use varistors or a series resistor with the diode.
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: PLC Relay Outputs Going Bad.
Interposing relays are cheap. So are fuses. If these valves are mains voltage I'd isolate them from the PLC through an interposing relay, regardless of the PLC relay's capability. PLC cards are too expensive to blow up, especially at Rockwell prices!
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: PLC Relay Outputs Going Bad.
Keith Cress
kcress - http://www.flaminsystems.com
RE: PLC Relay Outputs Going Bad.
Looks like 2 A is the continuous rating. Make/break rating is 28 VA.
RE: PLC Relay Outputs Going Bad.