SMOKE DETETOR IN GENERATOR ENCLOSURE

SMOKE DETETOR IN GENERATOR ENCLOSURE

SMOKE DETETOR IN GENERATOR ENCLOSURE

(OP)
Is it required to install smoke or heat detectors in outdoor soundproof generator enclosure? The generator will be located on building roof.

 

RE: SMOKE DETETOR IN GENERATOR ENCLOSURE

I certainly wouldn't.  "Smoke" detectors respond to a lot more than just smoke.

RE: SMOKE DETETOR IN GENERATOR ENCLOSURE

Normally use fixed temperature detectors. The more widely used "Rate of Rise" detectors will be prone to nuisance tripping in a generator enclosure.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: SMOKE DETETOR IN GENERATOR ENCLOSURE

Generator on a roof?  Sounds like trouble in so many ways.  

As for smoke detector - I'd advise against it - heat detectors are good as mentioned.  

But I don't know about applicable fire codes that could require it.  The local AHJ and fire marshal will have the last word - as usual.  

"An 'expert' is someone who has made every possible mistake in a very narrow field of study." -- Edward Teller

RE: SMOKE DETETOR IN GENERATOR ENCLOSURE

If you are in the US, I know of no provisions in either NFPA 72, the NEC or NFPA 101 that requires any detection in a generator enclosure. I am assuming you are talking of a standard sound attuating, weatherproof housing and not a roof penthouse of course.

As others mentioned your other issues of fuel storage and piping, etc..., might outweigh this issue.

RE: SMOKE DETETOR IN GENERATOR ENCLOSURE

NFPA 37 says "where provided" fire detection and alarm systems shall comply with NFPA 72 & 70.  If you do provide them you should have a look at 37 for what actions to take when the fire/smoked detection is tripped.  

It also says a fire risk evaluation shall be performed to assess whether a fire detection system is required.

RE: SMOKE DETETOR IN GENERATOR ENCLOSURE

Agree with Bribyk. An risk assessment is needed, but the local AHJ has the final say as dpc said.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources