recloser vs fuses
recloser vs fuses
From a utility's standpoint, what are the advantages of having customers install a recloser vs a fuse as their main protective device?
We are required by the utility to install a recloser to protect our primary meter service and the added cost for installing a recloser as opposed to fuses is significantly higher.
RE: recloser vs fuses
1) sensitivity - you are close to end-of-line and the utility feeder breaker may not distinguish the load current and end-of-line fault current
2) selectivity - utility wants to minimize the outage and also implement the fuse saving strategy
3) controllability - utility may want to lock you out via SCADA under certain circumstances
A recloser can trip all three phases, if all three phases aren't trip it can cause problems at some locations.
A recloser can also have an earth fault element which can be set below full load current. Fuses need to be rated above the full load current.
Alan
Democracy is two wolves and a sheep deciding what to have for dinner. Liberty is a well armed sheep!
Ben Franklin