Hi,
I have a proposal to upgrade a distribution line 4 km long that is now loaded up. The load has increased from the design load of 600 kVA to around 1.3 MW (almost 2X) so that they opted to install gensets to the newer buildings.
Other than going into a higher transmission voltage (13.8), is there any other economical ways to meet a load of around 1.3 MW (do away with the gensets)?
Any comment would be helpful.

Respectfully,

burnt2x

RE: Transmission at Medium Voltage 4160V

A lot more detail is necessary.  Like what voltage are you at now?  Distribution line suggests something higher than 480V, but 600kVA suggests something even possibly lower.

RE: Transmission at Medium Voltage 4160V

(OP)
David,
Thanks for the response.
Transmission voltage is currently at 4160V. Existing OH line is #4 ACSR, spaced 0.6 m horizontal. I have done initial investigations and the receving voltage at the 4 km end is at 3740V corresponding to a load of 76A/line. Any more load and the voltage goes down further. I was thinking upgrading to 13.8 kV. Just want to know if somebody has done similar upgrades.

RE: Transmission at Medium Voltage 4160V

4 km of insulators and a lot of labor to change them does increase the cost.
But this is probably still a good idea.
4160 is usually a wye system with 2400V transformers.
If you are using 4160 transformers in delta, you can increase the power by a factor of 1.73 by going to a wye connection, but I doubt that you are in delta.
As I understand it, the origin of the 4160 voltage was the reconnection of 2400 volt delta systems to increase capacity.
From experience, if you go to 12.7kV, 13.2kV, 13.8kV or any of the other voltages that you may find in the 15kV class, buy 7 transformers. You may have trouble finding an exact voltage match if you lose a transformer and need a replacement in a hurry. Have a replacement on hand and you will have time to shop for a reasonably priced replacement at the correct voltage if you lose a transformer.
Again, after consulting for a small independent utility that ran 13.2kV in a country that used 13.8kV on the main grid, I would first check what voltages are in use by surrounding utilities and I would check with the local distributors as to what voltage transformers are in stock.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Transmission at Medium Voltage 4160V

(OP)
waross, good points. I will keep those in mind.
And thanks a lot!

RE: Transmission at Medium Voltage 4160V

A voltage regulator and/or capacitors might also be enough to hold the voltage up enough to support more load.  Missed the 4160V in the title, just read the post.

RE: Transmission at Medium Voltage 4160V

You can re-conductor at the same voltage if it makes economic sense and the serving transformer has adequate capacity.  This would depend on expectation of future growth, condition of system, availability of capital, etc.  

 

"An 'expert' is someone who has made every possible mistake in a very narrow field of study." -- Edward Teller

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources