seemingly dumb vibration question
This question might come across as dumb, but......
When you're determining the natural frequency of a floor system you're supposed to use the natural frequency equation of something like 0.18*((g/delta)^0.5). My understanding is that this is true for something displaced by an amount delta and then suddenly released. Is this an accurate statement?
If so, why do you use the delta for the actual floor and not the delta imposed by the footfall? It seems the footfall is the only load causing a delta that is being removed. The delta caused by the DL of the floor is not being removed so how is it contributing to the natural frequency?
RE: seemingly dumb vibration question
From my understanding (famous last words...) it is true that the floor is rebounding from the footfall, but the footfall is no longer acting (hence the rebound) so it no longer applies. The delta obtained after the footfall is from m*g of the floor.
Does that help?
Natural frequencies are properties of the structure (function of stiffness and mass) and are usually completely independent of the load. The only except I can think of for linear systems would be members with axial load. For example, a string has a higher frquency if it's pulled tighter and a column has a lower frequency if it's in heavy compression and about to buckle.
The fn = 0.18*sqrt(g/Delta) is very handy for memorizing, but is an abomination otherwise because it causes confusion like in this case.
The actual equation for a simply supported beam is something like (don't have my book here and too lazy to google it) fn = pi/2*sqrt(mL^4/EI) -- I'm sure I lost a constant or something there. This is relatively difficult to remember, as I've illustrated here. m = a uniform line mass along the beam.
However, Delta = 5*w*L^4 / 384EI is easy to remember. If you plug in 5*w*L^4/384EI into the fn equation and manipulate it, you end up with fn = 0.179*sqrt(g/Delta).
w is nothing more than m * g, so you can see, w has to be the line load from the line mass attached to the beam.
Your formula is a handy approximation of the natural frequency of a simply supported beam. The true formula is ƒ=(N²π/2L²)√(EI/m), where N is the mode and N=1, 2, 3... For more discussion, see thread507-232284: Natural Frequency of a pinned-pinned beam. Only, ignore my post in that thread, as I posted the formula incorrectly. Hopefully, I got it right this time. With this formula, there is no deflection to be calculated. The natural frequency depends on the stiffness, the length, and the mass/unit length.
It is the reason why an army platoon breaks step when crossing a bridge. If they march across in step and happen to hit the natural frequency, the bridge could sway uncontrollably or even collapse if the excitation continues for long enough.
The following article may throw a little more light on the subject for a simple beam with equal cantilevers each end:
http
The natural frequency also depends on support conditions.
Best regards,
BA
http
The natural frequency of a beam is also dependent on boundary conditions, i.e. end restraint.
Best regards,
BA
Respectfully, this one part of your explanation isn't true. If a system is excited by a sinusoial force at frequency f, the response is sinusoidal at frequency f. Natural frequencies are special because when f equals one of them, the structure goes into resonance.
I agree with the rest of your explanation.
There's also a side discussion going on in this thread about footstep application and how that relates to natural frequencies. There is certainly structure-human interaction, but it is usually insignificant and therefore ignored except for maybe throwing a psf or two in there for humans on the structure. The major exceptions are very low frequency structures and very heavily loaded structures.
In very low freq structures, humans can subconsciously sense the vibration and synchronize footsteps to the response frequency to some extent. This is roughly what happened at the Millenium Footbridge in Europe a few years ago--look that one up on youtube.
Heavily loaded structures like balconies have so many people that one has to give the load a little more thought.
One thing to consider is that footstep application times are roughly 0.5 sec. to 0.8 sec. per step depending on step frequency and the right foot lands before the left leaves and vice versa. The slab vibrates through multiple cycles during the footstep application time. There's really no point to the argument that the footstep is only there some of the time. The truth is that one human on a typical structure doesn't interact with it enough to change how we compute fn. Just compute it as if the human isn't there. If there is a boatload of people, a crowd, or whatever, then engineering judgment must come into play.
Perhaps my wording was not precise. What I meant was that the natural frequency of a beam is independent of the exciting force. It can be calculated without reference to a particular exciting force.
If the exciting force is sinusoidal and happens to be frequency f which is equal to the natural frequency of the structure, then I agree that resonance will occur.
If a beam is deflected by a single force applied at midspan and the force is suddenly removed, the beam will vibrate at its natural frequency until the energy is dissipated.
Best regards,
BA
A rectagular stretched "panel" or "skin" would be more accurate - even a round drum cover is not appropriate. The ribs (joists) below the floor would create complicatins as well in the "skin" comparision, but less than assuming the whole floor is made up of beams.
At best, modeling the floor as a beam would introduce simplifications that invalidate the original intent of the analysis, wouldn't they?
In both of them, one computes the beam fundamental frequency as if it's isolated. Then do the same with the girder. Then, the European way to estimate the system two-way bending fundamental frequency by taking the min of the beam and girder freq. The predictions are usually pretty close to test results. The North American way is to use the Dunkerley's Equation to combine the beam and girder frequencies and predict the system natural frequency. This way results in frequency predictions that are usually on the low side by 10-20%.
Finite element modeling predictions of natural frequency are not always more accurate than the European way.