Water source heat pump condenser water pumps

Water source heat pump condenser water pumps

Water source heat pump condenser water pumps

(OP)
Can anyone come up with a good reason to use 2 condenser water pumps for each unit (on supply and return) on a water source heat pump system (geothermal)?

RE: Water source heat pump condenser water pumps

Pressure limitation on the geothermal source piping/tubing? I assume you mean a push-pull setup?  Is this a loop in the ground?  If so, it may have a significant pressure drop, and they don't want to put it under the high pressure needed to overcome the entire system pressure requirement.  All I can come up with!  More details please.   

RE: Water source heat pump condenser water pumps

I second Ross on that. I've seen the same set up.
Try to select a pump and see what kind of efficiency you will get. Low flow/high head application territory, reduce the head for a better, more efficient pump.

 

RE: Water source heat pump condenser water pumps

(OP)
Yes, it is a push-pull type setup.  

No, it is not my design.  I would use a main circulating pump and primary-secondary pumps for the individual heat pumps.  

Yes, it is a loop in the ground with 250' deep wells (U-tube type wells).

I don't see how 2 pumps in series reduces the head pressure on the piping.  It just reduces the head requirement for each pump.

 

RE: Water source heat pump condenser water pumps

If total system dP were 250 ft, and 125 ft of that were in the well tubing, the first pump only needs to be 125 ft.  Pressure in the tubing (at the bottom) would be 125 ft + 250 ft static = 375 ft or 162 psi, which is getting up there.  If you tried to push it thru the whole loop with just one pump ahead of the tubing, the pressure at the bottom of the loop would be 250 + 250 static = 500 ft or 220 psi.  These are high numbers, but the point is, material limitations may govern.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources