CAN ANYBODY HELP ME CALCULATE THE FUSE RATING FOR THESE PARAMETERS
INCOMING VOLTAGE=11KV
CAPACITOR BANK RATING= 200KVAR
KINDLY PROVIDE FORMULA USED.thanks

RE: capacitor bank fusing

Most utilities will have fusing tables for capacitor banks and transformers. Remember that capacitor voltage is proportional to the square of the voltage. Make allowances for over voltage operation.
Comparison example;- Canadian Electrical code.
Motors conductor ampacity> 100% plus 25% of largest motor.
Transformer conductor ampacity> 100% plus 25% of largest motor.
Capacitor conductor ampacity > 135% (CEC Rule 26-208,(1))

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: capacitor bank fusing

Even with the fusing table of utilities, how is the fuse rating calculated with a supply voltage of 11kv and a capacitor bank rating of 200kvar. Thanks.

RE: capacitor bank fusing

Vll=11kV
Var_3Ph=200kVar
Icap=200/(1.732*11)=10.5A

As per IEEE 1036-1992, Section 4.4.1, the minimum fuse size is no less than 125%~135% of the capacitor current.  In your case > 15E is ok
As per Canadian Code (OESC 23rd Edition) 26-210, the overcurrent device shall not exceeding 250% of the rated current of the capacitor.
We normally use 150~200% and also verify the capacitor damage curves obtained from the manufacture.

RE: capacitor bank fusing

200 kvar looks more like a single-phase can rating than a bank rating.  Is it really a 200 kvar bank or a 600 kvar bank?

RE: capacitor bank fusing

magoo2

Thanks for addressing that point.  200kVar really sounds odd for 3Ph...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources