Jobs

5 to 8% air entrainment

5 to 8% air entrainment

5 to 8% air entrainment

(OP)
If I am desiging a 100 feet long and 2 feet high retaining wall with 5 to 8% air entrained concrete for freezing and thawing, do I still need contraction joint?

RE: 5 to 8% air entrainment

The number of joints have nothing to do with air entrainment. It has to do with the amount of shrinkage and the amount of horizontal steel to resist the shrinkage forces.

With normal amounts of steel, I would recommend contraction joints at about 25 feet.    

RE: 5 to 8% air entrainment

I agree with jike, but in my experience, cracks form about every 10 ft in low retaining walls if a footing is cast first, then the wall.  If you want to control this cracking, space the joints at 10 ft centres.

RE: 5 to 8% air entrainment

Joints (ftng. matching wall) at 10 ft spacing sounds great to control (appearance) the cracks. I would also include a few 3/4" expansion joints (dowels w/end cap) to give your ret. wall a little room to move.  

RE: 5 to 8% air entrainment

I didn't mean joints in the footing at 10' centres.  Just in the wall.  The footing doesn't shrink as much as the wall, but does it earlier.  Who cares about cracks in the footing, you can't see them.

RE: 5 to 8% air entrainment

I will mention an additional criteria that is for low walls only: the spacing of joints should not exceed about 3 times the height of the wall. This corresponds a little closer to hokie66 (for low walls).

RE: 5 to 8% air entrainment

(OP)
Thank you guys. What would I do with out you?
By the way if the contractor does not pour this whole 100 feet long wall in one pour and does it in the stages with construction joints so than we will NOT need any contraction joint as there isn't a large chunk of concrete setting at any given time?
 

RE: 5 to 8% air entrainment

I did not read your original post thoroughly. A wall only 2 feet high is like a curb. 10 foot spacing makes sense.

I would still insist on 10 foot spacing for contraction joints but the contractor may substitute a construction joint for any contraction joint. Provide an expansion joint at 20 foot spacing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources