I have a 1000 kVA generator and a 1000 kVA transformer.
They both feed an open transition ATS in the main distribution board.
Since it is open transition, only 1 source is active at a time. The short circuit rating of the MDB is 30kA, sufficient for either source.
Now the client wants to substitute the open transition of the ATS to a closed transition ATS. The time both sources are online together during the closed transition is aroun 100 milliseconds. Will this require subsituting the whole MDB with another one with double the kA rating?
I have a 1000 kVA generator and a 1000 kVA transformer.
They both feed an open transition ATS in the main distribution board.
Since it is open transition, only 1 source is active at a time. The short circuit rating of the MDB is 30kA, sufficient for either source.
Now the client wants to substitute the open transition of the ATS to a closed transition ATS. The time both sources are online together during the closed transition is aroun 100 milliseconds. Will this require subsituting the whole MDB with another one with double the kA rating?






RE: Adding short circuit on closed transfer?
RE: Adding short circuit on closed transfer?
My feeling is: since they will be closed together for 100 milliseconds, what are the chances for a short circuit on the downstream network to happen at that particular moment in time?
Suppose we are working on generator because of a power failure, and the power has "returned", then downstream is fine because we are already using and supplying it, and the upstream is fine because the relays that sense the mains voltage return will not trigger the flip unless this side of the network has been diagnosed ok ... ?
RE: Adding short circuit on closed transfer?
"However, if the alternative source being paralleled is an onsite source, such as an engine-driven generator, short-circuit design calculations are usually based on this paralleled condition, if it exists for extended periods."
Please advise.
RE: Adding short circuit on closed transfer?
"An 'expert' is someone who has made every possible mistake in a very narrow field of study." -- Edward Teller
RE: Adding short circuit on closed transfer?
Also, does the generator have synchronism capabilities to prevent out of phase connection to the grid thru the 1000 KVA transformer. Is this a medical facility?
The ATS mfr. can lend guidance. I'm familiar most with Zenith/GE, Russelectric.
h
http://russelectric.com/
Regards . . .
Jim S. Nasby
RE: Adding short circuit on closed transfer?
RE: Adding short circuit on closed transfer?
It's an open transfer scheme. No synchronising problems.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Adding short circuit on closed transfer?
He wants to switch to closed transition ATS...
RE: Adding short circuit on closed transfer?
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Adding short circuit on closed transfer?
However Skokian is very correct that you need to examine your ground fault protection. Specifically, you need to determine if you are switching the neutral, and if your generator is neutral-bonded. Ideally you will have a solid neutral and leave your generator neutral unbonded. (It is bonded at the transformer through the solid neutral of the ATS.) If you have a switched neutral on the ATS, you need to have a neutral bond on the generator, but you may need to modify the operation of the ground fault system while in parallel operation. There are a variety of ways of accomplishing this depending on what type of ground fault detection you are using. It can get ugly.
Engineers are always honest in matters of technology and human relationships. That's why it's a good idea to keep engineers away from customers, romantic interests, and other people who can't handle the truth.
RE: Adding short circuit on closed transfer?
Thank you for your reply. Can you please indicate which standard mentions the 100ms limit?