what is the minimum kilowatt to use star delta connection for motors ?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
what is the minimum kilowatt to use star delta connection for motors
|
RE: what is the minimum kilowatt to use star delta connection for motors
In all cases wye-delta starters are inferior to any other reduced voltage starting method. It often causes many problems with no benefit at all.
Use a soft starter instead.
Keith Cress
kcress - http://www.flaminsystems.com
RE: what is the minimum kilowatt to use star delta connection for motors
RE: what is the minimum kilowatt to use star delta connection for motors
Way Out West, for motors operated at the facility service voltage, utilities generally have pat rules on this {like, say 40Hp} but for service at medium or high voltages, it's subject to engineering review.
I have worked on EU-originated process equipment where Y-D starting was applied to as low as 3Hp.