Shaft currents, insulating pipework flanges

Shaft currents, insulating pipework flanges

(OP)
If we have a large MV motor fixed speed with forced lubricated sleeve bearings and the motor manufature is offering insulated bearings DE & NDE ( with DE earth cable )Does the oil inlet & outlet pipework which has ANSI / DIN flanges, do these flanges have to be insulated. And if so how are are they insulated.

RE: Shaft currents, insulating pipework flanges

Only one of synchronous motor bearings is grounded and the other has to be insulated. So, also the metallic conduit connected with. In my opinion a flexible rubber conduit grease resistant and suitable to required pressure could be inserted close to the bearing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources