Measuring/Calculating Boiler Feedwater Heater Performance at Startup
At our coal fired facility we recently replaced four of six feedwater heaters. With the recent replacement I must measure/calculate the new heater performance. I will need to do this for startup conditions of which I do not have all the desired measured parameters needed to calculate TTD (terminal temperature difference) and DCA (drains cooler approach). The performance curves for TTD and DCA are given based on percent design feedwater flow and we are not measuring this. How can I calculate performance of the heater at intermediate loads without directly measuring the flow?
RE: Measuring/Calculating Boiler Feedwater Heater Performance at Startup
Best of luck!
<http://pepse.scientech.us/papers/1989section10.pdf>
For startup conditions, the conditons are likely dynamic and would need to include dynamic correction factors for thermal inertia of the tubesheeet, tubes, and shell.Not an easy task- it would seem more reliable to only determine the steady full load performance( heat exchanger efffectiveness e from the e-NTU method), work backwards to the apparent U*A for each zone ( desuperheater, condensing, subooler). Then pertube this model to determine steady state part load performance.
Every plant I've seen has a flow nozzle at the dearator outlet , so obtaining HP heater flows should be straightforward. The LP heater water flow may need to be calcualted based on a heat balance at the DA if a condensate pump flow element is not provided . Cascading drain flows would seem to be problematic- perhaps an ultrasonic flow device could be used to measure those flows.
I recently discovered we are adding triple redundant feedwater flow meters. So now I just need to figure out the correction factors for partial load performance. As my conditions will vary from design. I guess I'll thoroughly read through the document you posted davefitz to see if I can develop the correction factor for TTD and DCA for non-design conditions.
