Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...What a great service! This is the best site I've ever seen!!! It totally restores my faith in humanity when people take time out to help other people..."

Geography

Where in the world do Eng-Tips members come from?
steamdog (Chemical)
26 Feb 09 11:47
I have a very basic question.  A system with two 120VAC pressure switches needs to activate a 3-way air solenoid that would open the valve if either switch activates.  Can I just splice these wires together and attach them to the solenoid?
JLSeagull (Electrical)
26 Feb 09 12:40
Yes, and consider using screw terminals instead of splices if practical.

If the solenoid has a 120 Vac coil, it would be correct to series the pressure switch contacts that open to de-energize the solenoid.

Consider the pressure shelf positions.  If one switch is a low pressure switch, wire the common and normally open switch.  For the low trip the contact is open while sitting on the shelf thus below the trip condition.  The normally open contacts close after sufficient pressure exists.  If the other switch is a high pressure switch, you would wire the common and normally closed contact.  On the shelf the high pressure switch would not exceed the setpoint thus would be closed.  For a high pressure trip the contacts open after the pressure increases above setpoint.  Also, if the trips must be clear to start something, you could need a startup time delay with a contact across the low pressure switch contact that permits increasing to satisfactory pressure before applying the low pressure contact.

We also like additional contacts that generate alarms that indicate why the solenoid tripped.  Most of us prefer transmitters that can indicate the pressure thus provide indication of the measurement device failure.  Pressure switch failure can be undetected for a very long time without anyone being aware.
steamdog (Chemical)
27 Feb 09 12:56
Thank your JL.  This is an interesting application of a steam tunnel between two buildings that each have their own boiler. The valve with the two switches is normally closed on this connecting steam line.  Basically, if either boiler fails (thus a low pressure switch on either side of the valve), they want the valve to open to allow steam from one building to the other.  I was thinking of using a limit switch on the valve, they already know if the boiler is down, but this would give them positive indication that the valve is opened (or closed).
JLSeagull (Electrical)
2 Mar 09 8:06
Valve position switches or a position transmitter can also provide status of the valve.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close