Could anyone please tell me some information about the fault clearing time for 34kV substation?
Primary Protection + CB Trip = ?
Backup Protection + CB Trip = ?

Thank you!

RE: Fault clearing time?

Well, that's a rather general question, to which I can only give a general answer....

Primary protective devices should operate as quickly as possible, with backup devices picking up shortly thereafter (allowing time for primary protection to pick up first so as not to trip out more of your system than necessary to isolate the fault).

If you can provide more details about your specific system, I'm sure that I (or other forum members) can provide a more specific answer.

RE: Fault clearing time?

Assuming there is no generation on your system, the general answer is as follows -
- Primary protection will/should operate instantaneously, typically somewhere around say 20 mS
- Backup protection will be time delayed to coordinate with downstream protection; typically, this could be of the order of say 300-400 mS to give an adequate grading margin.

The time delayed protection must be set to protect the downstream equipment.  Transformers and cables have thermal withstand rating curves, and the protection must operate faster than these curves while operating slower than the downstream primary protection.

If there is generation involved, then there are additional concerns re stability and critical clearing time.  At this moment, I am working on a stability study for a client's 69/13.8 kV system and the "right" answer for them is 340 mS critical clearing time for 13.8 kV faults - any longer fault duration will cause the generators to become unstable relative to the utility system.

RE: Fault clearing time?

Suggestion: The answer may be even more involved if there are reclosers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources