Xd for leroy sommer generator
Xd for leroy sommer generator
(OP)
I´ll like to know the Xd for a leroy sommer generator, i thought that was 15 but i don´t remmenber
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Xd for leroy sommer generator
|
RE: Xd for leroy sommer generator
RE: Xd for leroy sommer generator
I think that your memory is failing you, Xd for an alternator of this size would be in the region of 2.85
X'd about 0.18
X"d about 0.13
RE: Xd for leroy sommer generator
Xd is sychronous reactance - and 150% - 300% is of the right order for this size.
Xd' is transient reactance, and 15% - 30% is the sort of value you see
Xd" is subtransient reactance, and can be say 5 - 20%
It all depends on the exact design and winding configuration
Xd' and Xd" are the ones you need most, for fault level calculations etc.
Why not ask Leroy Somer? www.leroy-somer.com
You will need the frame size and serial number from the nameplate
RE: Xd for leroy sommer generator
thanks very much