(OP)
Under new regulation of Z462 or NAFTA 70 what obligations manufacturing companies have to cope with this standard?
I work for a medium voltage utility manufacturer products.

RE: Manufacturing- Arc Flash

I guess it's very clear here; 110.16 Flash Protection

Quote:

"Switchboards, panelboards, industrial control panels, and motor control centers that are in other than dwelling occupancies and are likely to require examination, adjustment, servicing, or maintenance while energized shall be field marked to warn qualified persons of potential electric arc flash hazards. The marking shall be located so as to be clearly visible to qualified persons before examination, adjustment, servicing, or maintenance of the equipment.

RE: Manufacturing- Arc Flash

You need to obtain a copy of NFPA 70E-2009 to see the requirements for arc flash.  If your facility does not meet the limitations on the tables in NFPA 70E, then you will have to have an arc flash hazard analysis done for your facility.
You will also have to provide the proper PPE and training for personnel that may be exposed to arc flash hazards.

There is a ton of information at www.arcflashforum.com  This forum is solely devoted to arc flash.

RE: Manufacturing- Arc Flash

As a manufacturer, you need to be concerned about the electrical system in your plant.  Arc flash considerations for the gear that you sell to others is their concern.  The marking (labeling) has to be done as the result of a study for the specific installation, there is no way that the gear manufacturer could affix meaningful arc flash labels to the gear.

RE: Manufacturing- Arc Flash

(OP)
good point davidbeach. Thanks

RE: Manufacturing- Arc Flash

As a manufacturer- It's the purchaser's responsibility.

As a progressive manufacturer- Your customers have to meet arc flash requirements, so providing safer equipment is good business strategy.

RE: Manufacturing- Arc Flash

bacon4life,
That's a very nice way of taking a bigger slice of the market! If businesses are on the downtrend, your customers can always remember your brand for doing extra for the purchasers!  

RE: Manufacturing- Arc Flash

In the U.S. 110.16 (NEC) labeling requirement is typically met with a generic, non-site-specific, arc flash hazard warning label. For NEC compliance, it does not have to state specific exposure or hazard risk category. Most electrical equipment manufacturers provide this without asking.

If NFPA 70E compliance is the concern, then labeling would need to be installation-specific and an arc-flash study is required.

RE: Manufacturing- Arc Flash

alehman - I believe the 2008 NEC requires labels with either the flash protection boundary or actual exposure level stated on the label - no more generic labels are allowed.

RE: Manufacturing- Arc Flash

Quote (alehman):

I believe the 2008 NEC requires labels with either the flash protection boundary or actual exposure level stated on the label - no more generic labels are allowed.

The NEC article remains the same, the NFPA 70E now requires the panel to be labeled with either the Ei or the PPE required, but that is the responsibility of the equipment owner, not the equipment manufacturer. The manufacturer has no way of knowing what the EI will be, that depends on the system charaterstics.

Most OEM's put the Generic label of the gear, and that is it.

 

RE: Manufacturing- Arc Flash

Yes. NEC 110.16 is quoted by burnt2x above. There is no requirement for indicating exposure. 110.16 is followed by a fine print note that refers to NFPA 70E as a source of additional information, but FPN's are not part of the code.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources